Another compressor wiring question

drsung

Well-known member
Joined
Sep 27, 2011
Messages
274
Location
Louisiana
I just picked up a used 60 gallon Kobalt compressor and I am trying to figure out the correct way to wire it.

I have a 10/3 romex running into my garage being fed from a 30 amp breaker not within sight of the compressor. There is currently a L6-30R receptacle in the garage.

The compressor says it is 3.7hp and 15amp 220.

What is the best way to wire this thing correctly? I have attached the labels from the compressor and the motor.

What I would like to do is just wire a L6-30P and use the existing receptacle on one end and wire up the compressor end with some stranded 10/2. I think this is ok code wise since the motor is thermally protected and the plug would give me a disconnect. There is also a on/off switch on the compressor itself. What my research has me concerned about is if the NEMA plug can handle the horsepower rating.

Something like this:
https://www.lockingpowercords.com/Products/602-l6-30-power-cord-whips.aspx

-drsung
 

Attachments

  • IMG_20200216_151741.jpg
    IMG_20200216_151741.jpg
    92.2 KB · Views: 37
  • IMG_20200216_195855.jpg
    IMG_20200216_195855.jpg
    84.8 KB · Views: 37
Last edited:
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'd put in a new dedicated 20A 240V outlet and plug it in. That motor is not much more than 2hp. The 3.7 is hype.
 
Last edited:
OP
D

drsung

Well-known member
Joined
Sep 27, 2011
Messages
274
Location
Louisiana
I do not have the ability to run additional wire. I have to make do with the 10 gauge wire that is there in the best possible way. Are you saying put a 20A outlet on the existing 10 gauge wire being fed with the 30 amp breaker?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
No, do not put a 20A outlet on a 30A circuit. The L6-30P as you asked about will be okay if the motor does have thermal overload protection.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Don't get your wire designations mixed up. Romex that is 2 conductors plus ground is listed as **/2 w/Ground. The same in cord is **/3.
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
30 amp breaker is about right for that motor. Normally you could feed it with number 12 but since you are using a plug it must match the breaker.

Point is what you've got is close to perfect. For those suggesting a 20 amp breaker and plug, I would consider a 20 amp breaker to be borderline too small.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,599
Location
BC
My compressor has very similar power requirements. 15-16A @ 240V. It came with a 6-20P corded plug.

In general, I don't like twist-locks. Not only are they costly, but often end up with burnt prongs (in my experience, YMMV.) I prefer straight-blade, in an angle plug if possible. I might recycle a laundry plug/socket... not sure what NEC says about that.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Laundry are not wired correctly,,,, doesn't mean guys havnt used them though. I agree a lot of them run on 20. There isn't a fundamental cost difference and I have some 30 so would have to buy 20,,,, so 30 it would be.
 