Another GFCI question

bassbone52

Well-known member
Joined
Jan 7, 2011
Messages
516
Location
Central Indiana
I recently installed some exterior soffit lights. I ran power to a new switch for the lights from a garage circuit protected by an GFCI receptacle upstream from the new switch. I had a length of Romex connected to the load side of the switch. The circuit was energized but the switch was open. I cut the Romex and the GFCI tripped. Why did this happen?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Most likely another load was connected after the gfci recept. When you cut the cable, momentarily you created a path between neutral and ground.

In doing so, that load's neutral current split and some traveled on the ground wire instead of all on the neutral.

Gfci sensed that difference between hot and neutral current and tripped.
 
To avoid these ads, REGISTER NOW!
OP
B

bassbone52

Well-known member
Joined
Jan 7, 2011
Messages
516
Location
Central Indiana
Excellent explanation. Thanks to both of you. In fact, there is a garage refrigerator between the GFCI and the new switch.
 