Another heater size dilemma

Dart53

Member
Joined
Feb 16, 2008
Messages
10
Location
South Coast, MA
Hello all,

I'm about to install a Hot Dawg or similar type ceiling mounted heater to my unheated garage here in MA and am struggling (maybe overthinking:willy_nil) to determine the right size.

The garage is 22'x23'x8.5' with two 9'x7' insulated ovhd doors, four dbl-hung windows(48 sf) and an insulated man-door(17.8 sf). The walls are 2x4 construction and are sheetrocked. Only one wall, the 23' one without the ovhd doors is insulated (R-13). The ceiling is sheetrocked and insulated (R-30). The concrete floor is uninsulated.

I've received several estimates from contractors proposing heaters from 30K to 60K Btu's. I've checked out a couple online calculators but they seem pretty general and don't take into account doors or windows. Using them I get 30K-45K heaters.

Should just go with the average and get a 45K heater? Any suggestions?
 
To avoid these ads, REGISTER NOW!

dogdas

Well-known member
Joined
Oct 24, 2014
Messages
94
45 is big and a 60 is stupid. With that size you can get away with the 30. You only have 4300cf. I have on my attached a 75 at 9000sf and that is fine. The last thing you want is the unit cycling too much. That just beats the **** out of things. Your garage is insulated well so I would go with a 30 and be done with it, its not that cold in MA.
 