ALinCarolina
Well-known member
I have installed a single head Mini-split in the past and everything went well but I am now in the process of installing a 3 head unit and I have two questions. The outside unit has the 3 high and low fittings for each of the 3 inside units as expected but there is also another service port on the suction side above the set of 3. So I assume I need to nitrogen pressure test and deep vacuum each of the 3 circuits individually? What do I do about the bigger service port at the top? It seems to me that the one up top doesn't go anywhere much other than to the accumulator and I assume is already charged with refrigerant. The installation manual makes no mention of course.
The second question concerns the adapters sent with the unit, It is a 12/9/9 BTU unit and the suction flares on the outdoor unit are 3/8. The line set for the 12K head is 1/2" suction. They sent 3 adapters: 3/8 to 1/2 flare which would be used for the larger line set. There is a piece of flared copper tube inside the adapter. I assume that this stays in place so that there is soft copper between the brass flare surfaces. But I have never used one of these and wanted to make sure it wasn't there just for their testing. Thanks.
The second question concerns the adapters sent with the unit, It is a 12/9/9 BTU unit and the suction flares on the outdoor unit are 3/8. The line set for the 12K head is 1/2" suction. They sent 3 adapters: 3/8 to 1/2 flare which would be used for the larger line set. There is a piece of flared copper tube inside the adapter. I assume that this stays in place so that there is soft copper between the brass flare surfaces. But I have never used one of these and wanted to make sure it wasn't there just for their testing. Thanks.