Here are the parameters:
I have an outbuilding that I want to run a 100A feed to from my home.
The home has a 200A (AL) entrance.
The run would be approximately 150 feet. Of that, 45 would be in the basement and then approx. 92 feet of conduit under the attached garage and continuing underground to the detached building..leaving 13 feet of make in wiring for inside the outbuilding.
The conduit is 1 1/2 inch PVC.
The twist is that years ago I purchased a Quincy QR series Duplexing Air Compressor with a 200 Gal tank & (2) 7.5 3-phase motors 230/460V...22.2A/11.1A each.
Since I don't have 3-phase power and after looking at Rotary phase Converters, I came across a smokin' deal on a 33KW Onan Diesel GenSet powered by a 4 cyl. Cummins complete with a 120 Gal attached tank...Wife takes husband to hospital to have head checked.
I figure set the GenSet to 120/240 3-phase...power the compressor when I need it and then have it ready for stand-by when the power goes down for the house.
Talked to an electrician...
1. Genset to a 3-phase transfer switch. Switch up to feed Quincy, switch down to send the power to the second transfer switch.
2. Second transfer switch. Would have the house feed in the middle. Switch up powers the panel in the outbuilding(during normal conditions from the house),switch down would be the feed from the GenSet. I would have to take the house off line at the main before energizing the GenSet feed.
I would also need (2) grounding rods and separated neutral/ground bars on the outbuilding panel...right?
I told the electrician that I was leaning toward CU for my feed instead of AL.
He suggested 2-2-2-8 CU if that was what I was thinking.
COntacted several jobbers and was really pushed toward 2-2-4-6 (AL) twisted direct burial. Is that the trailer feed wire? Price around 200.00
The 2-2-2-8 (CU) was around 520-600.00 WOW!
Is the 2-2-4-6 adequate or am I just living in the old days when most wiring was copper.
Thanks for the space.
I have an outbuilding that I want to run a 100A feed to from my home.
The home has a 200A (AL) entrance.
The run would be approximately 150 feet. Of that, 45 would be in the basement and then approx. 92 feet of conduit under the attached garage and continuing underground to the detached building..leaving 13 feet of make in wiring for inside the outbuilding.
The conduit is 1 1/2 inch PVC.
The twist is that years ago I purchased a Quincy QR series Duplexing Air Compressor with a 200 Gal tank & (2) 7.5 3-phase motors 230/460V...22.2A/11.1A each.
Since I don't have 3-phase power and after looking at Rotary phase Converters, I came across a smokin' deal on a 33KW Onan Diesel GenSet powered by a 4 cyl. Cummins complete with a 120 Gal attached tank...Wife takes husband to hospital to have head checked.
I figure set the GenSet to 120/240 3-phase...power the compressor when I need it and then have it ready for stand-by when the power goes down for the house.
Talked to an electrician...
1. Genset to a 3-phase transfer switch. Switch up to feed Quincy, switch down to send the power to the second transfer switch.
2. Second transfer switch. Would have the house feed in the middle. Switch up powers the panel in the outbuilding(during normal conditions from the house),switch down would be the feed from the GenSet. I would have to take the house off line at the main before energizing the GenSet feed.
I would also need (2) grounding rods and separated neutral/ground bars on the outbuilding panel...right?
I told the electrician that I was leaning toward CU for my feed instead of AL.
He suggested 2-2-2-8 CU if that was what I was thinking.
COntacted several jobbers and was really pushed toward 2-2-4-6 (AL) twisted direct burial. Is that the trailer feed wire? Price around 200.00
The 2-2-2-8 (CU) was around 520-600.00 WOW!
Is the 2-2-4-6 adequate or am I just living in the old days when most wiring was copper.
Thanks for the space.