The central air for my house stopped working a few days ago. Its an older Williamson unit - house was built in 84, and I don't know if its been replaced since. Symptom - on the outside unit, the fan runs but the compressor does not. I heard it buzz, but it doesn't run. Once the fan is going you can't hear the buzz anymore.

I found the schematic, and it looks like the red wire between the compressor run capacitor and the contactor burned out. The spade connector is a loose fit, but I don't know if it was loose before the wire burned up, or not. I also found evidence of critters living in there.

At the store this morning I bought a new cap. 40uF, 370V, $16 - made in China but I'll roll the dice and I didn't have a choice.

1) Is there anything special about the wire used here? Is normal 14G stranded an OK replacement?

2) The cap isn't bulged, but the terminals are corroded and loose where the fire happened. Is it correct to replace the cap?

3) A contractor was at the store with me. He looked at the wire and told me to suspect my microwave, oven and refrigerator... and he told me to call my insurance company. When he left the clerks told me to ignore him, that he's been having a bad day. But still, am I going to burn the place down if I goof this up?

I have a referral to a reputable tech if required.

Advice anyone? Many thanks!
 

Attachments

  • 100_0895.jpg
    100_0895.jpg
    145.5 KB · Views: 47
  • 100_0896.jpg
    100_0896.jpg
    140.2 KB · Views: 45
  • 100_0891.jpg
    100_0891.jpg
    135.6 KB · Views: 34
To avoid these ads, REGISTER NOW!

Cuda

Well-known member
Joined
Apr 13, 2010
Messages
244
Location
Utah
I'd say your doing all the right things. If it does work for you after replacing the cap. I'd throw an amp meter on your compressor line to see what it's drawing. If it's higher than the name plate you could be needing a new unit.
 
To avoid these ads, REGISTER NOW!

ebasista

Well-known member
Joined
Dec 25, 2008
Messages
56
You're on the right path here. Caps go bad all the time. With a unit as old as yours I would have bought a kick start/hard start capacitor to give the compressor a bit more juice to get her moving.

Remember this though, this compressor is ancient, and if you do get her running (very likely) you should be planning on an HVAC upgrade in the near future.


Replace the wires with the same gauge and stranded. I've seen burned out contactors where critters decide to call them home and likewise corrosion/loose wires causing them to melt.

I hope you disconnected the power and left it off as soon as you had the problem.....reason being that the buzzing sound is the compressor getting power and trying to start......if it keeps doing that for too long the compressor will eventually burn out.

At this point you have nothing to lose, so good luck
 
OP
M

mikeatrpi

Well-known member
Joined
Jan 10, 2006
Messages
383
Location
Home
Update -

I installed the new cap and replaced that one section of wire. I also used some dielectric grease on the connectors and pinched the old ones to create a tighter connection. I'm happy to report - its working again!!!!

We probed the old cap, and it was a short between the terminals. That's probably what caused this wire to flame out.

Thank you all!
 