To avoid these ads, REGISTER NOW!

Any assistance with buck boost transformer?

_strickland

Member
Joined
Nov 26, 2021
Messages
9
I fully realize most people here would say just hire an electrician and I'm willing to do that if no one feels comfortable providing input.

I need to install a buck-boost transformer for my ac condenser because the incoming voltage from my electric company is too high, usually hovers around 250-251V. Using the buck-boost I can take it down to 234. I know the H wires are for the line voltage, the X wires are for the low voltage to buck down. I've also identified the wiring diagram I need to follow to accomplish what I'm trying to do, but I admittedly don't read wiring diagrams well at all. Could anyone give me a step-by-step of which wires to tie together?
 

Attachments

  • wiring_diagram3.jpg
    wiring_diagram3.jpg
    17.7 KB · Views: 23
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,246
Location
NJ
250v is close to the upper limit. I wouldn't go out and buy a b-b xfmr b/c of that.
Here is a snip-it from a condenser unit spec:
1685745996436.png

If I had a b-b xfmr sitting around, I might install it - but not my 1st priority. You would also need it sized (KVA rating) for the load.

A downside to having a b-b installed is, if the voltage sags in your area, then the b-b could compound that problem.

I have seen the voltage at my house as high as 254V and I'm running the same condenser for years.
 
OP
S

_strickland

Member
Joined
Nov 26, 2021
Messages
9
Thanks everyone for the replies. My main reason for asking about it was that my condenser is a variable speed, and the drive systems on them are the most sensitive to too much, or too little voltage. It's often one of the main reasons why variable units fail.
 
OP
S

_strickland

Member
Joined
Nov 26, 2021
Messages
9
The spec on the unit is the same as any other, 208/230. Most all bb are either 12/24 or 16/32, and dropping 16 would get me the closest to 230.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
The spec on the unit is the same as any other, 208/230. Most all bb are either 12/24 or 16/32, and dropping 16 would get me the closest to 230.
I should have been more specific.
What is the upper limit if the units operating range? 208/230 doesn't really tell us anything especially since 230v isn't a thing in single phase service in the US
 
OP
S

_strickland

Member
Joined
Nov 26, 2021
Messages
9
I should have been more specific.
What is the upper limit if the units operating range? 208/230 doesn't really tell us anything especially since 230v isn't a thing in single phase service in the US

The service manual says 253. I have observed the incoming voltage getting that high a couple times before.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,234
Location
Modesto, CA
I fully realize most people here would say just hire an electrician and I'm willing to do that if no one feels comfortable providing input.

I need to install a buck-boost transformer for my ac condenser because the incoming voltage from my electric company is too high, usually hovers around 250-251V. Using the buck-boost I can take it down to 234. I know the H wires are for the line voltage, the X wires are for the low voltage to buck down. I've also identified the wiring diagram I need to follow to accomplish what I'm trying to do, but I admittedly don't read wiring diagrams well at all. Could anyone give me a step-by-step of which wires to tie together?
wiring a buck-boost is easy

per your diagram, line input 1 goes to H1 as well as 1 leg of the output

Line input 2 goes to X2/X4 spliced together.

then you splice X1 to X3, H4 & the other output leg

next splice H2 & H3

But i would call your PoCo first and let them know the voltage is running a bit high. See what they say. could be a distro regulation issue
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,234
Location
Modesto, CA
I should have been more specific.
What is the upper limit if the units operating range? 208/230 doesn't really tell us anything especially since 230v isn't a thing in single phase service in the US
all motors are rated 115v/200v/230v/460v for system voltages of 120/208/240/480v
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
The service manual says 253. I have observed the incoming voltage getting that high a couple times before.
How often do you check the voltage? I have checked mine a grand total of one time, and that was only because I put a new service in and before I turned the main on, wanted to make sure I didn't do anything stupid. I couldn't even tell you what that voltage was.
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,375
Location
Hunterdon County NJ
Best advice is to read my post #5…….. You pay big bucks to the utility so call them and they will most likely come out for free to "investigate" the potential problem.


BTW! Hopefully the OP used an accurate meter and checked the accuracy with a second meter.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,234
Location
Modesto, CA
Call the utility company and have them look into this "issue"……… I would avoid using a BB transformer.

BTW! Be thankful you don't have low voltage.
yup

had a trouble call years ago where appliances were tripping breakers.

After arriving and discussing the issue with the homeowner, I discovered the voltage to the mobile home main service panel was 228v with no load. when the microwave or AC turned on the voltage dropped even lower which caused them to draw more power than usual. The microwave breaker ended up tripping. If i ran the oven, the voltage drop was even worse.

I explained what was going on and the homeowner told me that Profit Gouge & Execute (PG&E) had been out there for months trying to fix power issues in the park. At one point they had to replace equipment and while doing so ran the entire park off of generators. I explained to her that it looks like the problems werent resolved and she needed to reach out to the electric provider & let them know there are still issues. no clue what happened after that....
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
NEMA uses a different criteria for motors to determine voltage limits than general circuits.
It can be +/- 10% without causing immediate damage to the motor, but caution that running it continuously at the voltage will shorten the life of the motor.
 
To avoid these ads, REGISTER NOW!
Top Bottom