According to his build thread , N. California. Might be an IT guy.415v 3Ø? what country are you in?
weird how he titled the thread 415v... its been changed now to 208vAccording to his build thread , N. California. Might be an IT guy.
lg
no neat sig line
Yea i was mistaken, it is only 120/208 that would be coming in if i went 3 phase.weird how he titled the thread 415v... its been changed now to 208v
Yes a possibility as "grows" are legal at this address with the appropriate permits.Is there any chance that an indoor farmer will rent your metal building once you install power?
but 415v is not even an available system voltage in the US. it would be 480vYea i was mistaken, it is only 120/208 that would be coming in if i went 3 phase.
Data centers in the US are using 415Y/240V because more equipment can be run then with 120V circuits & most IT equipment can run either voltage. There is no prohibition for 240V equipment in a non residential occupancy. Less need for transformers to get 120V cuts the heat load too.but 415v is not even an available system voltage in the US. it would be 480v
Yes but those are a special animal and the data centers are probably providing the step-down transformers themselves via a primary HV feed from the PoCo.Data centers in the US are using 415Y/240V because more equipment can be run then with 120V circuits & most IT equipment can run either voltage. There is no prohibition for 240V equipment in a non residential occupancy. Less need for transformers to get 120V cuts the heat load too.
Agreed it's a odd beast, also.Yes but those are a special animal and theyre probably providing the step-down transformer themselvesvia a primary HV feed from PoCo
I highly doubt theres any PoCos in the US that are gonna supply 415v/240v to a residential shop or small commercial property and that was my point.
I was in IT when some of our "big iron" needed 3 phase. That is where I learned what little I know about it. Like large blowers (fans) that run on 3Ø can blow the wrong direction ! Simply swap 2 wires (phases).According to his build thread , N. California. Might be an IT guy.
In the early 2000s, I was in charge of 3 different data centers in SE MI. Some were small, but one as pretty darn good sized. (Maybe 5 tennis courts ?). Most were feed by 208V 3Ø. Some used higher voltage. The equipment we ran was form the 80s/90s. It either used 208V 3Ø or 120V single phase. Nothing used 240V. Well, we did have one high speed laser printer that said it needed 240V, but it had an internal transformer that had an input tap for 208V.Data centers in the US are using 415Y/240V because more equipment can be run then with 120V circuits ...
This would be more recent & would be on a Amazon scale, where the economics would pay.In the early 2000s, I was in charge of 3 different data centers in SE MI. Some were small, but one as pretty darn good sized. (Maybe 5 tennis courts ?). Most were feed by 208V 3Ø. Some used higher voltage. The equipment we ran was form the 80s/90s. It either used 208V 3Ø or 120V single phase. Nothing used 240V. Well, we did have one high speed laser printer that said it needed 240V, but it had an internal transformer that had an input tap for 208V.
This would be more recent & would be on a Amazon scale, where the economics would pay, and the A/C load would require more then 208V.
Have family that had 3ph available, ran it into the shop, used it for about 20yrs then disconnected it as it was more per month vs 240v 1ph power after the shop uses changed of course.If 3 phase was available at my house I would have had 3 phase power ran to it.
415V 30A 3ph circuit gets you 17.3 KW to the rack, instead instead of 8.6 for 208V. Power is the limiting factor in high-performance DC density, followed by removing the heat. There are GPU based servers that use 2500W in 2U, for a rack full you'd need 50 KW.In the early 2000s, I was in charge of 3 different data centers in SE MI. Some were small, but one as pretty darn good sized. (Maybe 5 tennis courts ?). Most were feed by 208V 3Ø. Some used higher voltage. The equipment we ran was form the 80s/90s. It either used 208V 3Ø or 120V single phase. Nothing used 240V. Well, we did have one high speed laser printer that said it needed 240V, but it had an internal transformer that had an input tap for 208V.
What you need is load dependent. I would say 120/208 is more common for small commercial but if you pick the wrong one all it takes later is a dry type transformer to make the one you need.Well heard back from the power company, these are my 3 options for the property:
120/240 volt single phase
120/240 volt three phase
120/208 volt three phase
Guessing i will be doing the 120/240 3 phase, but any reason i should consider 208?
be careful with the stinger leg/hi-leg, which is 208v to neutral. This means you will only have 2 phases that can power 120v loads. you will also have to use straight rated breakers (240v to ground) instead of slash rated breakers (120v to ground) due to the 208v to ground on the stinger legWell heard back from the power company, these are my 3 options for the property:
120/240 volt single phase
120/240 volt three phase
120/208 volt three phase
Guessing i will be doing the 120/240 3 phase, but any reason i should consider 208?
Well heard back from the power company, these are my 3 options for the property:
120/240 volt single phase
120/240 volt three phase
120/208 volt three phase
Guessing i will be doing the 120/240 3 phase, but any reason i should consider 208?
Hmm, the power company is stating if i go 120/208 i need to buy the panel from them, is this not common?What you need is load dependent. I would say 120/208 is more common for small commercial but if you pick the wrong one all it takes later is a dry type transformer to make the one you need.
ok, something i didnt consider, thanks!be careful with the stinger leg/hi-leg, which is 208v to neutral. This means you will only have 2 phases that can power 120v loads. you will also have to use straight rated breakers (240v to ground) instead of slash rated breakers (120v to ground) due to the 208v to ground on the stinger leg
thanks for the input!I'd stay away from the 120/240 3-Phase(Delta) as you're limited on the number of 120V breakers you can have due to the hi-leg(stinger/wild/etc.).
If it were me I'd go with 120/208V 3-Phase out of all these options.
Think the only extra is my initial cost as i need to run the service line from the transformer, once there its there.If this happens to be vacant at any time, and you wish to keep the lights/heat on.... Do check if 3-phase is going to cost you extra.
Its not uncommon to see commercial buildings around here with dual services. (The 3-phase only get 'lit up' if the tenant wants to take that on.)
I suspect they meant the meter socket/service disconnect, not the panel.Hmm, the power company is stating if i go 120/208 i need to buy the panel from them, is this not common?
Only some PoCo's supply meter cans, the customer is usually responsible for supplying & wiring everything except the meter, in addition to being required to comply with code, the installation must meet PoCo specs.I suspect they meant the meter socket/service disconnect, not the panel.
Only some PoCo's supply meter cans, the customer is usually responsible for supplying & wiring everything except the meter, in addition to being required to comply with code, the installation must meet PoCo specs.
Well found out that its a full transformer and engineering from the PoCo if i want the 208/120. Cost of 35K+ so that is now out of the question.I suspect they meant the meter socket/service disconnect, not the panel.
make sure you can source the straight rated breakers that you will need for 240 Delta. you cant use slash rated 120/240v breakers due to the 208v to ground hi-leg. The breakers need the higher rating for ground faults as the voltage and energy is higher. this would be for any double pole and 3 pole breakers since single pole breakers cannot go on the hi-leg unless you want to let out the magic smoke on 120v equipment.Well found out that its a full transformer and engineering from the PoCo if i want the 208/120. Cost of 35K+ so that is now out of the question.
So now down to 240/120 3ph and 240/120 1ph. So its looking like the 240/120 3ph is my choice. Waiting to hear back if they can do it 400a now.