Section 210.52(A) - (2/3/2016)
Section 210.52(A) outlined required receptacle spacing for dwelling unit such that no point measured horizontally along the floor line in any wall space is more than 6 ft from a receptacle outlet. It also defined wall space in 210.52(A)(2) as any space 2 ft or more in width and unbroken along the floor line, space occupied by fixed panels in exterior walls, and space afforded by fixed room dividers. The NEC handbook includes the following in section 210.52(A) "The word usable does not appear at all in 210.52 as a condition for determining compliance with the receptacle spacing requirements. As an example, to correctly determine the dimension of the wall line in a room, the wall space behind the swing of a door is included in the measurement. This does not mean that the receptacle outlet has to be located in that space, only that the space has been included in the wall-line measurement."
Does an opening in floor (doorways, fireplaces and similar openings) resets the receptacle placement requirement such that each unbroken wall space is considered as an individual separated wall spaces and that receptacle is needed in each individual separated wall space?
A wall is separated by (2) doors such that the wall space between the doors is 2'-0", does this section of the wall required dedicated receptacle? Does a receptacle 1'-0" from the edge of the other side of either door meets the intent of the code such that any point on the 2'-0" wall is no greater than 6'-0" along the floor line from a receptacle?
A wall include a bump out in the center, the bump out is measured along the floor line such that is it 1'-0" depth and 2'-0" width. The walls to the left and right of the bump out are 4'-6" each. Is 1'-0" depth floor lines required in the wall space calculation as it is less than 2'-0"?
A receptacle is place 1'-0" away from the handle side of the door opening. The wall space for the wall behind the door swing is 2'-0". Is a receptacle needed on the 2'-0" wall?
Yes.
Yes. This is a separate wall space and requires a receptacle. No, a receptacle that is 1'-0" from the edge of the other side of either door doesn’t meet the code intent.
Yes.
Yes, if the wall space in question is a separate wall space.