Arc Fault breakers tripping in the rain

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
Home: 2006 with Siemens breaker panel.

Last night after it had been raining for a few hours we lost power to two bedrooms.

I went outside and found two tripped AFCIs (Master bedroom and 2nd bedroom). Couldn't reset them. Noticed the bottom of the breaker box wasn't dry. Door doesn't have a seal?? Hmmm.

After it had stopped raining I removed the breaker cover panel. Wires from the breakers loop down and are touching the bottom of the box (NEC?). Bottom of the box is a mixture of standing water (1/32") and wet sloppy mud.

Wiped out the mud and water and called it day since it was now getting dark.

Plan for today:

Drink coffee so I can wake up.

Blow out the box with compressed air.

Investigate how water got in.
Add a seal to the door?

Unplug everything in the two rooms
Check outlets for heat damage

Remove wires from AFCIs:
- Inspect for insulation damage
- Confirm breakers will reset
- Check for shorts (continuity) between said wires and to ground

What else?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
You dont know if they tripped because of an Arc Fault or an overload.

Looks like those have an arc fault indicator. Did you look at that before resetting?

The water wont make them trip since theyre not GFCI.
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
Last edited:

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,833
Location
Southern Oregon
If you have any working AFCIs in the panel, swap one to determine if its the breaker or the wiring.
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
If you have any working AFCIs in the panel, swap one to determine if its the breaker or the wiring.

I do have a working AFCI, but there are two different AFCIs that won't reset.

Both breakers could have failed at the same time or thereabouts, but I'm thinking it's more likely that the two circuits have a wiring fault in common. Logical?

Once the wife is done cooking up a storm and doing laundry I'll take the cover off and see if the breakers will reset when disconnected.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
I'm blown away that breaker panels - especially ones with GFCI and AFCI breakers - are still allowed to be mounted outside. :wtf:
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
I looked at my neighbor's breaker panel, it's the same model, and his does have a seal.
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,273
Location
Coastal NJ
Those breakers look weathered. Change them and go from there. Crack one open and see what the insides look like. You may have other breakers getting tired if these look bad inside.
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
Got it figured it out. Several loose connections, a chafed wire, and a bad breaker. The AFCIs don't snap onto to the bus bar like I'm used to. They slip right off with two fingers.
I'm going to swap all three of them out with CAFCI.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Is the panel overhead or underground service? Next question is there a hub or closure cap on top? The reason I ask is depending on the age of that panel there may be a missing gasket for the hub or cap allowing water to enter the enclosure, but some Siemens panels do not require a gasket due to the design.
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
It's underground. There is a cap on top with one screw in the middle. I'll pull it off and see what I've got.
 
OP
4

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,280
Location
back 40
Is there a code spec for wire to wire resistance (insulation)? Checking for shorts I had one pair at 35 megohm instead of infinity.
 
Last edited:

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I'm blown away that breaker panels - especially ones with GFCI and AFCI breakers - are still allowed to be mounted outside. :wtf:

I was shocked (haha, get it) the first time I saw outside mounted electrical panels on a TV show. There's a dry spot just on the other side of that wall for Pete's sake!

Outside mounted plumbing gets me too, but at least that's more understandable if there's no risk of freezing.
 