Are All Breaker Boxes This Tidy?
jeepxj
is it ok to use that left box as the raceway for the right one?
rlitman
Long Island
what about all the hots?
I don't see the point in that. A smooth radius on the grounds lowers the impedance to ground, which helps to divert surge energy. Higher impedance on a hot wire doesn't hurt anything.
Neat wiring makes later repairs easier, Service Loops should have been included. Service loops can be made neatly.
Agreed. When I measure in a hot wire in a panel, I'll cut it long enough so that the breaker can be moved in the future to any other position on the bus without splicing, and then figure out how to neatly contain the extra length.
rlitman
Long Island
The more I look at it, the less I like it. It will be impossible to modify anything in there.
In a residential install, I agree. In the commercial stuff I deal with at work, it's fine, because there are service loops in the wiring trough where everything comes in from a few feet above the panel. You do end up cutting a lot of zip ties when you make any changes though.
Debcrow
New Mexico
The powerplant where I worked all of the old cloth and lead covered wire from the 1920's up was neat like that.
All of the later plastic covered wire was a lot more random.
Common work expectations change with time, combined with more complicated wiring and multiple additions to existing junction boxes.
In the end it all worked whether it was neat or not.
I removed the covers from the breaker boxes when I was painting the garage wall. These are the tidiest breaker boxes I've ever seen. When the electrician added the breaker for the island electric cooktop he told me this was about as precise work as he had ever seen.
the ground wires all braided together is actually not tidy and will make things difficult in the future. shouldve ran them to individual lugs or double up at the very least. also i bet that lug theyre terminated in is not rated for all those wires.
Looks Pretty but I bet there are things not to code. As there usually is Something...
plenty not to code here. Bryant and SQ D breakers in an ITE/Siemens panel, too many ground wires under that one lug.....
All those ground wires twisted up and landed under one lug. Hate that ****.
yup total trash install...
mike93lx
Richmond, VA
Those grounds though...absolute nightmare in any situation requiring rework
exranger06
CT
On the left side is a black neutral wire with white tape wrapped around it, which is technically a code violation. When running individual conductors in conduit, you're not allowed to re-identify wires like that, unless they're #4 or larger. Those wires look smaller than #4.
PCustoms
VT
What's with the 2x4 between the panels?
Appears to be 2 pieces....
Mzungu