Are arc fault breakers required everywhere?

Ross/Kzoo

Well-known member
Joined
Oct 22, 2013
Messages
2,191
Location
Richland Mi.
I found this online:

"All 120 volt / 15 or 20 amp branch circuits supplying outlets (includes both lighting outlets and receptacle outlets) in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc fault circuit interrupter. This means that nearly every habitable space in new homes are required to have this protection."

At $43-50 a pop these aren't cheap. Is there some place in the home where this isn't required?
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
I found this online:

"All 120 volt / 15 or 20 amp branch circuits supplying outlets (includes both lighting outlets and receptacle outlets) in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc fault circuit interrupter. This means that nearly every habitable space in new homes are required to have this protection."

At $43-50 a pop these aren't cheap. Is there some place in the home where this isn't required?
Bathrooms?

Not sure what you have is 2014 code but Kitchens are added in 2014.

Garages don't need AFCI either
 

BJ42LX

Well-known member
Joined
Dec 29, 2010
Messages
2,811
Location
WNY
How does arc fault and ground fault play together? Are they compatible or do you get one or the other?

Is it acceptable to install GFCI outlets on arc fault protected circuits?

Are there AFCI and GFCI breakers?
 

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
I love the things.

Every time you turn on a vacuum cleaner the breaker has to be reset. :lol:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
OK, what does that mean for me? Is it just the bedrooms?

Yes IIRCC

How does arc fault and ground fault play together? Are they compatible or do you get one or the other?

Is it acceptable to install GFCI outlets on arc fault protected circuits?

Are there AFCI and GFCI breakers?

AFCI and GFCI are 2 different animals.

AFCIs are for arcing faults that can light something on fire. An example situation could be a frayed lamp cord sitting under a bed arcing. The arc is intermittent so the regular breaker doesnt trip.

GFCIs are for current leaking outside the circuit. An example would be a 2-wire metal tool with a hot wire touching the housing. Because theres no grounding, the regular breaker doesnt trip. The user touches the frame at the same time as grabbing or touching a grounded water pipe. Current flows from the tool through the user and into the water pipe back to the panel. The current isnt enough to trip the breaker but COULD BE high enough to kill the person.

As far as use, it depends on the circuit and area feeding.

There is combination devices that have both types of protection:

http://w3.usa.siemens.com/powerdist...eakers/pages/dual-function.aspx?ismobile=true
 
Last edited:

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
847
Location
In between MA and PA
OK, what does that mean for me? Is it just the bedrooms?

Nope.

The 2011 NEC requirements are: NEC 210.12(A) Where Required. All 15A or 20A, 120V branch circuits in dwelling units supplying outlets in family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas must be protected by a listed AFCI device of the combination type.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Nope.

The 2011 NEC requirements are: NEC 210.12(A) Where Required. All 15A or 20A, 120V branch circuits in dwelling units supplying outlets in family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas must be protected by a listed AFCI device of the combination type.

Ok my bad. I must be confusing 2008 and 2011 NEC
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Required anywhere your protecting the circuit without a gfci. If your state adopts the 2014 code then they will be required everywhere
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
I've ran every corded power tool I have (including miter saw and tile saw) on my AFCI's.....have yet to trip one.

But it did detect a broken wire.
 

bgeery

Active member
Joined
Jul 2, 2013
Messages
43
Location
Yucca Valley, CA
Or use power tools with arcing brushes. Pull the trigger on a drill and trip the breaker.
The peanut gallery on every electrical forum always bashes AFCI and GFCI.

Other than some first gen stuff, the CAFCI (and GFCI) breakers don't commonly nuisance trip. If they are tripping, they are doing their job. Your equipment is likely worn out, or defective. The last thing I would suspect would be a defective breaker.

I have CAFCI and GFCI on every single 15/20 Amp circuit in the house, and I've had one nuisance trip in the last 2 years. The worst I can say about them is they will trip sometimes when power is restored after an outage, but that is a design feature to protect their electronics, not a defect.

BTW, check eBay for the best prices (about half of retail)
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
The peanut gallery on every electrical forum always bashes GFCI and GFCI.

Other than some first gen stuff, the CAFCI (and GFCI) breakers don't commonly nuisance trip. If they are tripping, they are doing their job. Your equipment is likely worn out, or defective. The last thing I would suspect would be a defective breaker.

I have CAFCI and GFCI on every single 15/20 Amp circuit in the house, and I've had one nuisance trip in the last 2 years. The worst I can say about them is they will trip sometimes when power is restored after an outage, but that is a design feature to protect their electronics, not a defect.

BTW, check eBay for the best prices (about half of retail)

There is nothing wrong with GFCI's, AFCI's never did what they claim & the customers became the beta test, which is what I have issue with, the idea is good but the crooks behind it all should be shot for thievery, namely UL, NFPA, and the manufacturers, & others, it should have been much further developed before being required.


With Ebay, you have no assurance that the product is genuine, the product is costly enough that the ChiComs could be counterfeiting them. Remember the fake SQ D QO breakers? The ChiComs do supply most of the worlds counterfeit merchandise.
 
To avoid these ads, REGISTER NOW!

Whitworth

Well-known member
Joined
Dec 26, 2011
Messages
2,084
After I had a new home built in 2005, the first thing I did was replace those arc fault breakers and fling them in the trash.
 

bgeery

Active member
Joined
Jul 2, 2013
Messages
43
Location
Yucca Valley, CA
There is nothing wrong with GFCI's, AFCI's never did what they claim & the customers became the beta test, which is what I have issue with, the idea is good but the crooks behind it all should be shot for thievery, namely UL, NFPA, and the manufacturers, & others, it should have been much further developed before being required.
Youtube has test video of CAFCI breakers being demonstrated. They work as intended *now*, and stop potential fires, so it's pointless to rehash the problems of the first gen devices. First gen electronics always have bugs/hitches, but you don't find them until the devices are out in the real world, being used with real world equipment.

With Ebay, you have no assurance that the product is genuine, the product is costly enough that the ChiComs could be counterfeiting them. Remember the fake SQ D QO breakers? The ChiComs do supply most of the worlds counterfeit merchandise.
Sure, there is a risk, but there is enough info out there to detect the counterfeits now. Pay full retail if it makes you more comfortable.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Did you know that if you touch the ground and neutral in a light with the switch off it still trips the breaker,not much of an arc there. Can't wait till the price comes down
 

woodzy

Well-known member
Joined
Oct 16, 2011
Messages
248
Location
Se Michigan
This varies by inspector. I just built a house (finished in December 2014), and before I started I talked to the inspector. He said he would require AFCI on all bedroom circuits only. GFCI on bathroom, kitchen, laundry, garage, basement, and outside. Everything else could be regular circuit breakers. He did require GFCI on the lights over the tub shower but I think that is overkill.

Some other things you should talk to them before you start. Do they require tamper resistance outlets everywhere? A few years ago, I purchased a GFCI tamper resistance outlet, and it was almost impossible to plug something into it. I replaced it with a regular one and my wife was happier. The new house has 100% tamper resistance outlets (even though the inspector said he would not check them) but they must have perfected them since they work very well.

Also, when it comes to outside outlets, they now according to code require in-use covers. Some people claim that these turn in to wasp hotels but my inspector said he would not look very close at those as most people don’t really like them.
 
OP
R

Ross/Kzoo

Well-known member
Joined
Oct 22, 2013
Messages
2,191
Location
Richland Mi.
This varies by inspector. I just built a house (finished in December 2014), and before I started I talked to the inspector. He said he would require AFCI on all bedroom circuits only. GFCI on bathroom, kitchen, laundry, garage, basement, and outside. Everything else could be regular circuit breakers. He did require GFCI on the lights over the tub shower but I think that is overkill.

Some other things you should talk to them before you start. Do they require tamper resistance outlets everywhere? A few years ago, I purchased a GFCI tamper resistance outlet, and it was almost impossible to plug something into it. I replaced it with a regular one and my wife was happier. The new house has 100% tamper resistance outlets (even though the inspector said he would not check them) but they must have perfected them since they work very well.

Also, when it comes to outside outlets, they now according to code require in-use covers. Some people claim that these turn in to wasp hotels but my inspector said he would not look very close at those as most people don’t really like them.


Thanks, that helps a lot.
 

Beemer533

Well-known member
Joined
May 9, 2014
Messages
2,057
Location
Syracuse, NY
... The worst I can say about them is they will trip sometimes when power is restored after an outage, but that is a design feature to protect their electronics, not a defect.

....

Which is an awesome feature when hooked up to a fridge or freezer or other "critical" service like an alarm panel, phone system, etc...
 

bgeery

Active member
Joined
Jul 2, 2013
Messages
43
Location
Yucca Valley, CA
Which is an awesome feature when hooked up to a fridge or freezer or other "critical" service like an alarm panel, phone system, etc...
If you want to avoid CAFCI breakers potentially safety tripping, when power is resumed after an outage, I believe the solution is to install a whole house surge suppressor at the main panel. At least that seems to have cured the issue for my house.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Fyi, the state of Michigan residential code supercedes the nec. You will be working from the latest adopted addition of the mrc which I think is either 2005 or 2008. It is a little more relaxed with afcis. As it is I believe only bedrooms.
As far as getting rid of them, why. You paid 40 to 50 dollars for something to just throw away? Makes cents to me. They work. If you get them online, make sure that they are combination afcis, the will protect against arc faults and over current, not ground fault.
As a point of thinking I'd like to see them make panels with afcis mains, it would solve all problems and keep things relatively less expensive that way.
 
OP
R

Ross/Kzoo

Well-known member
Joined
Oct 22, 2013
Messages
2,191
Location
Richland Mi.
I talked with the electrical inspector today and in Mi. AFCI's are only needed in bedrooms and for smoke detectors unless the dwelling has more than 2 units.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Fyi, the state of Michigan residential code supercedes the nec. You will be working from the latest adopted addition of the mrc which I think is either 2005 or 2008. It is a little more relaxed with afcis. As it is I believe only bedrooms.
As far as getting rid of them, why. You paid 40 to 50 dollars for something to just throw away? Makes cents to me. They work. If you get them online, make sure that they are combination afcis, the will protect against arc faults and over current, not ground fault.
As a point of thinking I'd like to see them make panels with afcis mains, it would solve all problems and keep things relatively less expensive that way.


According to several links Ive found MI is on NEC 2011

And that is NOT what a combination AFCI is. A combination AFCI detects both parrallel AND series arcing faults. Regular AFCIs ONLY detect parrallel faults.

An AFCI main? :eek: Yeah that would be a great idea. Have a fault on a branch circuit and loose power to the whole house! smh :rolleyes: I think not! Just out of curiosity, how does that solve ALL problems? IMO, that would create more issues!!


Whoops! Better check your reference. It says 2011 for MI... :lol_hitti
 
Last edited:

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
I'd like to see them make panels with afcis mains, it would solve all problems.

What?... :shocking:...Like they don’t already cause enough grief, if the main breaker were AFCI, then the entire house loses power with a simple nuisance trip.

Don’t see how that solves any problems? :willy_nil :headscrat
 

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Last edited by wyliesdiesels; Today at 05:42 PM.

An AFCI main? :eek: Yeah that would be a great idea. Have a fault on a branch circuit and loose power to the whole house! smh :rolleyes: I think not! Just out of curiosity, how does that solve ALL problems? IMO, that would create more issues!!

Way to go wyliesdiesels, change/edit your post so now mine looks like I simply copied yours…:lol_hitti

Today, 04:37 PM

What?... :shocking:...Like they don’t already cause enough grief, if the main breaker were AFCI, then the entire house loses power with a simple nuisance trip.

Don’t see how that solves any problems? :willy_nil :headscrat
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Way to go wyliesdiesels, change/edit your post so now mine looks like I simply copied yours…:lol_hitti

Honestly, that wasnt my intention. I was at work on break when i started editing my post before u posted your comment. Break was over and I didnt have time to finish and hit save. Came back after work and finished it!
 