2011laramie
Well-known member
Hello,
I'm just trying my hand at some manual J calcs.
My shop is 44x64x16, and will be divided into a 24x44x16 bay that I will heat full time, and then a 40x44x16 bay that will be heated when i need to be out there.
This is in Alberta where it easily hits -40F. with a room target of 50F
shop details for the small bay
2x8 studs on 16" centres going to use roxul mineral wool. assuming effective R value of R22.
has roughly 56q ft of windows, going to assume R4, they are double pane low E with Argon I believe
Overhead door is 168 sq ft of R16
63sq ft of man door (1 single to outside, and a double door to other bay), Assume R10.
the roof will be blown in R60
the floor has 2" of foam board under the slab, then 1.5" down the footing on the inside and 2" down the footing on the exterior.
the interior divider wall is also 2x8 but on 24" centres.
so time for math.
1889ft2 of 2x8 wall. U=.0454
1056 of roof U= .0167
1056 of floor U=??? i don't know what to use?
168 of OH door U=.0625
56 windows U=.25
63 man door U=.1
Q=UxAxdelta T
.0454x1889x90 = 7718
.0167x1056x90 = 1587
.0625x168x90 = 945
.25x56x90 = 1260
.1x63x90 = 567
total BTU is 12077.
now for the big bay.
only going to consider a heat loss out 3 wall cause the other wall will always be at 50. technically it would actually be a heat gain into this bay.
total wall area = 2683 ft2 of 2x8 wall.
windows = 64ft2
Overhead doors = 368ft2
man door 21ft2
roof = 1760ft2
floor = 1760ft2
Q=UxAxdelta T
.0454x2683x90 = 10962
.25x64x90 = 1440
.1x21x90 = 189
.0167x1760x90 = 2645
.0625x368x90 = 2070
total for this bay 16006btu
That gives me a grand whopping total of 28083 btu/hr. No I haven't accounted for air leakage or the loss through the floor. because I don't know how to account for those values. what is the general rule?
are these numbers close or did i mess up royally. when The manual J calcs are final, how much extra does a person add so that the heater isn't running 24 hrs a day to meet the load?
I don't have a solid plan, but what my plan as of right now is to put a 50000 btu boiler in and run the slab on the small side, then run a glycol fan coil unit in the big side when i want heat over there. I picked this route because i read that gas unit heaters shouldn't be left to go below 5C for corrosion.
Any professionals got any input to this??
I'm just trying my hand at some manual J calcs.
My shop is 44x64x16, and will be divided into a 24x44x16 bay that I will heat full time, and then a 40x44x16 bay that will be heated when i need to be out there.
This is in Alberta where it easily hits -40F. with a room target of 50F
shop details for the small bay
2x8 studs on 16" centres going to use roxul mineral wool. assuming effective R value of R22.
has roughly 56q ft of windows, going to assume R4, they are double pane low E with Argon I believe
Overhead door is 168 sq ft of R16
63sq ft of man door (1 single to outside, and a double door to other bay), Assume R10.
the roof will be blown in R60
the floor has 2" of foam board under the slab, then 1.5" down the footing on the inside and 2" down the footing on the exterior.
the interior divider wall is also 2x8 but on 24" centres.
so time for math.
1889ft2 of 2x8 wall. U=.0454
1056 of roof U= .0167
1056 of floor U=??? i don't know what to use?
168 of OH door U=.0625
56 windows U=.25
63 man door U=.1
Q=UxAxdelta T
.0454x1889x90 = 7718
.0167x1056x90 = 1587
.0625x168x90 = 945
.25x56x90 = 1260
.1x63x90 = 567
total BTU is 12077.
now for the big bay.
only going to consider a heat loss out 3 wall cause the other wall will always be at 50. technically it would actually be a heat gain into this bay.
total wall area = 2683 ft2 of 2x8 wall.
windows = 64ft2
Overhead doors = 368ft2
man door 21ft2
roof = 1760ft2
floor = 1760ft2
Q=UxAxdelta T
.0454x2683x90 = 10962
.25x64x90 = 1440
.1x21x90 = 189
.0167x1760x90 = 2645
.0625x368x90 = 2070
total for this bay 16006btu
That gives me a grand whopping total of 28083 btu/hr. No I haven't accounted for air leakage or the loss through the floor. because I don't know how to account for those values. what is the general rule?
are these numbers close or did i mess up royally. when The manual J calcs are final, how much extra does a person add so that the heater isn't running 24 hrs a day to meet the load?
I don't have a solid plan, but what my plan as of right now is to put a 50000 btu boiler in and run the slab on the small side, then run a glycol fan coil unit in the big side when i want heat over there. I picked this route because i read that gas unit heaters shouldn't be left to go below 5C for corrosion.
Any professionals got any input to this??