Armor clad wire?
Bert_
NW Iowa
Either a handy box extension or my personal favorite 4 square extension to handy box, makes a better transition to the box in the wall.
Blazinzuk
Afton Wy
I'm such a newb on electrical stuff lol. I have seen those even. Thanks man
dogdog
It was not allowed even for AC / MC wires to be exposed in my neck of the woods.. Not 100% sure about the NEC.
dscheidt
Not where subject to damage. Same rules as NM-B. That probably should be done in EMT or wiremold.
Zeke
Same rules apply for AC and NM cable. I think fastened to the sides of framing members and above the bottoms of joists, etc. should fly. It has to run parallel to framing but is allowed to span perpendicular to rafters and joists if pulled though or fastened to the bottom at each. The key is it in a protected space and secured properly. If you don't think it would pass with NM, it probably won't with AC.
PhysicsDude
Dallas, TX
Most electricians will prefer to use an extension ring. Its generally not ideal to have an electrical connection on the cover of the box, just makes it harder to stuff the wires in the box, service it, etc. Not against code or anything like that.
If it were me in my shop just to hook up a couple lights, I think the way you're doing it is fine.
ctgoodman
Salisbury, NC
When using the armored cable the cladding must be grounded to a metal box. You cannot put that into a plastic box. I also think the clamp on the cover is for romex and not the proper one for mc. I know here anti short bushings are required with mc and that clamp is not correct type to use with an anti short bushing. Just had my shop wired. I'll try to post a pic or two tomorrow.
Manufacturers do not require anti-shorts with MC cable
Blazinzuk
Afton Wy
So irregardless of it being AC wire ( armor clad). It still should be in conduit when exposed like that?
dogdog
Last I know, It was a NO GO.
I think there is a reference of that here or there some years back I don't remember the exact post.... I just remember when I upgraded the meters and panels, the inspector came and check, ***** about those expose AC/MC wires by the panel and the electricians had to fix that real quick in 45 minutes or so... before they would pass the inspections..
Norcal
Nor does the NEC.
The OP's cable is Metal Clad, MC.
____________________________________________________________
I do question the connector used by the OP, is it a MC or NM connector?
ctgoodman
Salisbury, NC
No this is just a local thing with our county inspectors. I think it had something to do with a large development in the area that had some fires caused by damaged wire and these where not used. I like the idea of using them to keep the wires from rubbing the cut mc or the connector and shorting out. My contractor said he always uses them as a CYA measure.
ctgoodman
Salisbury, NC
No that cable does not have to be in conduit. I’m not sure if this cable is even allowed in a conduit. You may have to transition it in a box if you have a need to use conduit. I do know it is never to be used in wet location. So it cannot be underground even in a conduit.
alfredeneuman
Fullerton, CA
Romex 2 screw connectors have open throats.
2 screw connectors for AC and MC cables have closed throats, with a small hole in the center for the wires to go through, with scalloped edges on the edges so you can see the anti-short bushings through them.
If you look at them from the outside, you can't tell the difference.
MC cable has a wrap of mylar around the wires, AC does not.
They're required with AC cable.
I phoned the tech folks at Southwire some years ago, and asked why the include the bushings with rolls of MC cable, if they're not required.
The answer was "just as an added degree of protection above and beyond what's required".
PoorOwner
CA
I see these used under eaves and parking lot lights all the time. May have been a special cable called teck?
How high are these cables located? Last I checked you are allowed to run nm cable mounted high enough in a garage, where it would be considered in a protected location. Could be subject to AHJ interpretation though.
alfredeneuman
Fullerton, CA
Southwire uses red and black stripes on the armor of it's 12-3 MC cable.
2 wire uses only black .
4 wire uses black, red, and blue.
From the looks of it, it's 3 wire MC cable.
TEK cable isn't available or listed in the US.
PoorOwner
CA
So mc is allowed in the open like parking garage and security lights but AC is not?
Bert_
NW Iowa
The key here is subject to damage. Just because it is ran on the surface does not mean it's subject to damage.
Horizontal run 4' high along a garage wall is probably subject to damage. 6-7'+ is less likely to be but as always it depends on the situation.