I am adding additional power to my attached garage in order to run my wood working equipment. The original plan was to run 6AWG to a 60amp sub panel, but after some investigating I realized this was going to get quite expensive. I have room in the 200 amp service panel in the basement so my next thought was to run three branches to the garage (1 -240V and 2 120V). I realized quickly that the run was rather long to the farthest outlet in the garage so I started to research voltage drop and proper wire size. I have figured out that for the table saw I could use 12-2 romex pulled through conduit based on the calculation below:
Table Saw - 15A @ 240V 100ft away from panel with maximum voltage drop of 3%
(AMPS x FEET)/(PERCENT VOLT DROP x VOLTAGE) = VDI
(20 x 100)/(3*240) = VDI = 2.77 which is what leads me to 12-2 romex
I will also be running a dust collector which has max draw of 14 amps on a 15 amp circuit @ 120V. Same calculation for 15amp circuit is below
(15 x 100)/(3*120) = VDI = 4.16
This means I need 10AWG wire for the 120V circuits.
I will need two 120V circuits as I will be running the dust collector along with a planer (15A rated)
My questions are as follows:
Am I better off to run stranded wire for the 120V circuits? All Circuits? (I have heard it will deliver cleaner power to the equipment and in turn run better?)
Can i run 12AWG instead of 10AWG if I use stranded since the voltage drop is less?
Should I be running 20A 120V circuits if equipment is rated at 15A? If so do I calculate the wire gauge based on 15A or 20A?
Like most people I am on a pretty tight budget and I have plans to build a dedicated building in about 5 years so I am trying to do this on the cheap, but I don't want to sacrifice safety for a few extra bucks. Any help on this would be greatly appreciated.
Table Saw - 15A @ 240V 100ft away from panel with maximum voltage drop of 3%
(AMPS x FEET)/(PERCENT VOLT DROP x VOLTAGE) = VDI
(20 x 100)/(3*240) = VDI = 2.77 which is what leads me to 12-2 romex
I will also be running a dust collector which has max draw of 14 amps on a 15 amp circuit @ 120V. Same calculation for 15amp circuit is below
(15 x 100)/(3*120) = VDI = 4.16
This means I need 10AWG wire for the 120V circuits.
I will need two 120V circuits as I will be running the dust collector along with a planer (15A rated)
My questions are as follows:
Am I better off to run stranded wire for the 120V circuits? All Circuits? (I have heard it will deliver cleaner power to the equipment and in turn run better?)
Can i run 12AWG instead of 10AWG if I use stranded since the voltage drop is less?
Should I be running 20A 120V circuits if equipment is rated at 15A? If so do I calculate the wire gauge based on 15A or 20A?
Like most people I am on a pretty tight budget and I have plans to build a dedicated building in about 5 years so I am trying to do this on the cheap, but I don't want to sacrifice safety for a few extra bucks. Any help on this would be greatly appreciated.