Brandon_oma#692
Well-known member
Hi,
I am in rural Illinois.
I have an attached garage (connected to the house by a enclosed breezeway) that I need to upgrade the electric in. I have 100 amp service to the house. Cutler hammer CH breaker panel. 90 amp or less breaker to feed the garage sub panel. House is concrete block construction basement to roof with aluminum siding. Garage is stick built and bare studs inside.
Household electric loads.
Electric dryer
Electric water heater
TV's, microwave, 1 window air conditioner, general household stuff for a small 3 bedroom house.
Plan is to abandon the existing 20 amp garage circuit. Run 2-2-2-4 aluminum wire mhf in 1-1/4 Pvc conduit from panel to panel. From house to garage. Exit left of panel along interior basement wall approx 6'. LB to turn and go out thru basement block wall above exterior ground and below a deck approx 8'. Sweep up above deck and LB to enter garage approx 2'. LB up to new panel in garage approx 5'.
Garage panel. Thinking Eaton 100 amp panel with CH breakers so it is compatible with the house breakers. Use 100 breaker in this panel for the main since it comes with the panel and wire is protected by the smaller breaker in the main house panel.
Lighting circuit with mainly outlets for plug in led fixtures plus 2 regular bulbs.
20 amp 120 general circuit.
20 amp 120 circuit for 4 exterior outlets 1 per corner of garage.
50 amp 240 welder circuit
?? Amp 240 circuit to hardwire the synchrowave (match breaker in main panel that feeds this panel)
50 amp 240 circuit with 14-50 exterior
15 or 20 amp 120 dedicated for current air compressor need to check amp rating
?? Amp 240 circuit for lathe
Currently have the 40 amp 240 breaker that was for an electric stove in the house main panel wired to a 14-50 exterior outlet on the house. I plug a cord into that and run it to the driveway or garage to do anything 240v. Garage is a mess of extension cord to run lights and everything else. Only 2 outlets along the back wall. Lights flicker bad when I use the compressor or automotive scissor lift.
Electric stuff in garage.
120 air compressor
120 automotive scissor lift
120 motorcycle lift
240 welder Miller synchrowave 250
240 lathe less than 3hp
Angle grinder, bench grinder, battery chargers, led lights, flourscent lights, incandescent lights, security cameras, Christmas lights, big fan and medium fan...... . general stuff
Looking for a plasma cutter will be 240
Looking for a 240 mig welder unless I can borrow my Dad's indefinitely.
Need to add a fan in the gable to draw out the hot air in the summer
Might upgrade air compressor in the future
Currently everything "works" as long as I run the air compressor and automotive scissor lift off the "cord of doom". Not correct and anytime I do that it is plugged in to use and unplugged immediately after. This is why a am looking at getting a sub panel asap.
Where are the holes in this plan? The synchrowave welder has been happy on the 40 amp but I am using it at the low end of the amperage capability for this machine.
I am in rural Illinois.
I have an attached garage (connected to the house by a enclosed breezeway) that I need to upgrade the electric in. I have 100 amp service to the house. Cutler hammer CH breaker panel. 90 amp or less breaker to feed the garage sub panel. House is concrete block construction basement to roof with aluminum siding. Garage is stick built and bare studs inside.
Household electric loads.
Electric dryer
Electric water heater
TV's, microwave, 1 window air conditioner, general household stuff for a small 3 bedroom house.
Plan is to abandon the existing 20 amp garage circuit. Run 2-2-2-4 aluminum wire mhf in 1-1/4 Pvc conduit from panel to panel. From house to garage. Exit left of panel along interior basement wall approx 6'. LB to turn and go out thru basement block wall above exterior ground and below a deck approx 8'. Sweep up above deck and LB to enter garage approx 2'. LB up to new panel in garage approx 5'.
Garage panel. Thinking Eaton 100 amp panel with CH breakers so it is compatible with the house breakers. Use 100 breaker in this panel for the main since it comes with the panel and wire is protected by the smaller breaker in the main house panel.
Lighting circuit with mainly outlets for plug in led fixtures plus 2 regular bulbs.
20 amp 120 general circuit.
20 amp 120 circuit for 4 exterior outlets 1 per corner of garage.
50 amp 240 welder circuit
?? Amp 240 circuit to hardwire the synchrowave (match breaker in main panel that feeds this panel)
50 amp 240 circuit with 14-50 exterior
15 or 20 amp 120 dedicated for current air compressor need to check amp rating
?? Amp 240 circuit for lathe
Currently have the 40 amp 240 breaker that was for an electric stove in the house main panel wired to a 14-50 exterior outlet on the house. I plug a cord into that and run it to the driveway or garage to do anything 240v. Garage is a mess of extension cord to run lights and everything else. Only 2 outlets along the back wall. Lights flicker bad when I use the compressor or automotive scissor lift.
Electric stuff in garage.
120 air compressor
120 automotive scissor lift
120 motorcycle lift
240 welder Miller synchrowave 250
240 lathe less than 3hp
Angle grinder, bench grinder, battery chargers, led lights, flourscent lights, incandescent lights, security cameras, Christmas lights, big fan and medium fan...... . general stuff
Looking for a plasma cutter will be 240
Looking for a 240 mig welder unless I can borrow my Dad's indefinitely.
Need to add a fan in the gable to draw out the hot air in the summer
Might upgrade air compressor in the future
Currently everything "works" as long as I run the air compressor and automotive scissor lift off the "cord of doom". Not correct and anytime I do that it is plugged in to use and unplugged immediately after. This is why a am looking at getting a sub panel asap.
Where are the holes in this plan? The synchrowave welder has been happy on the 40 amp but I am using it at the low end of the amperage capability for this machine.