Looking for some assistance making some decisions regarding the subpanel I will be adding in my attached garage. I am getting an electric vehicle (Tesla Model S 75D
) this week and need to get a charging outlet installed.
Requirements for charging will be either a 50A (NEMA 14-50) outlet or a 60A circuit for the Tesla 'wall charger'. Also will be adding 3-4 20A 120V circuits for outlets, 1 15A 120V circuit for lighting and 1 15A 120V circuit for my yet-to-be-installed hanging NG furnace. No other 240V loads at the moment, but would like to get a larger air compressor in the near future.
A little more far-fetched would be to add a second EV in the future that would have similar 240V demand. Although it would likely be set up to load-share with the Tesla.
1-man shop. 3-car garage. Doing mostly car repairs (30gal air compressor, 120V) and woodworking (table saw, router table, dust collector - all 120v).
Main panel (200A, SQD QO) is in the unfinished basement. Subpanel will be 100A SQD QO 24 slot main breaker. Wire run will be approximately 50ft and will consist of: up from the main panel to the floor joists, ~30' along floor joist, 90deg turn to go thru garage wall ~5', then 90 deg turn up and into the subpanel.
Option #1 - Full 100A using #3 CU (3-3-3-8) THHN run in 1-1/2 PVC conduit. This would be the most work and most expensive. Would also be the most future-proof.
Option #2 - 85A (90A breaker) using #4 CU (4-4-4-8) THHN run in 1" or 1-1/4" PVC conduit. Same amount of work but less expensive. Maybe a little less work handling the smaller conductors.
Option #3 - 90A using AL 2-2-2-4 SER, no conduit. Least expensive and I'm assuming less work, although would have to wrestle with the larger conductors inside the panels.
I think I would prefer running conduit just for the sake of protection. But I suppose I could run the SER in conduit just for the last portion run into the garage.
I was leaning towards option #1 but the cost differences are pretty significant.
Thanks,
Jim
) this week and need to get a charging outlet installed.Requirements for charging will be either a 50A (NEMA 14-50) outlet or a 60A circuit for the Tesla 'wall charger'. Also will be adding 3-4 20A 120V circuits for outlets, 1 15A 120V circuit for lighting and 1 15A 120V circuit for my yet-to-be-installed hanging NG furnace. No other 240V loads at the moment, but would like to get a larger air compressor in the near future.
A little more far-fetched would be to add a second EV in the future that would have similar 240V demand. Although it would likely be set up to load-share with the Tesla.
1-man shop. 3-car garage. Doing mostly car repairs (30gal air compressor, 120V) and woodworking (table saw, router table, dust collector - all 120v).
Main panel (200A, SQD QO) is in the unfinished basement. Subpanel will be 100A SQD QO 24 slot main breaker. Wire run will be approximately 50ft and will consist of: up from the main panel to the floor joists, ~30' along floor joist, 90deg turn to go thru garage wall ~5', then 90 deg turn up and into the subpanel.
Option #1 - Full 100A using #3 CU (3-3-3-8) THHN run in 1-1/2 PVC conduit. This would be the most work and most expensive. Would also be the most future-proof.
Option #2 - 85A (90A breaker) using #4 CU (4-4-4-8) THHN run in 1" or 1-1/4" PVC conduit. Same amount of work but less expensive. Maybe a little less work handling the smaller conductors.
Option #3 - 90A using AL 2-2-2-4 SER, no conduit. Least expensive and I'm assuming less work, although would have to wrestle with the larger conductors inside the panels.
I think I would prefer running conduit just for the sake of protection. But I suppose I could run the SER in conduit just for the last portion run into the garage.
I was leaning towards option #1 but the cost differences are pretty significant.
Thanks,
Jim