Chip, I copied this from Duravent.com:
VENT TOP INSTALLATION
The location selected for the vent top can have a
significant influence on proper draft performance. On a
windy day, nearby obstructions such as a wall or tree can
create a zone of high pressure. When the vent cap is
located in these high pressure zones, the vent becomes
highly susceptible to windy conditions and may tend to
backdraft. In those cases when the vent must be installed
in a position less than 8 feet from a wall, parapet, or other
obstruction, the vent cap must be located at least 2 feet
above the obstruction.
High pressure zones can also be created by wind striking
the roof itself. For roofs from flat to 7/12 pitch, the vent
cap should be positioned at least 1 foot above the roof
surface. As indicated in Figure 43, measure the vertical
distance between the roof surface and the lowest discharge
opening on the vent cap.
As the roof pitch increases above 7/12, the roof begins to
act more like a wall, and the pressure zone increases. To
compensate for this, it is necessary to increase the height of
the vent. The steeper the roof, the greater the vent height
required to avoid the high pressure zone. Refer to the table
in Figure 43 listing minimum heights for roof pitches
greater than 7/12.
Figure 43
Gas Vent Termination Table
Roof Pitch........................Minimum Height
Flat to 7/12 . . . . . . . . . . . 1.0 feet*
Over 7/12 to 8/12 . . . . . . . . . 1.5 feet
Over 8/12 to 9/12 . . . . . . . . . 2.0 feet
Over 9/12 to 10/12. . . . . . . . . 2.5 feet
Over 10/12 to 11/12 . . . . . . . 3.25 feet
Over 11/12 to 12/12 . . . . . . . . 4.0 feet
Over 12/12 to 14/12 . . . . . . . . 5.0 feet
Over 14/12 to 16/12 . . . . . . . . 6.0 feet
Over 16/12 to 18/12 . . . . . . . . 7.0 feet
Over 18/12 to 20/12 . . . . . . . . 7.5 feet
Over 20/12 to 21/12 . . . . . . . . 8.0 feet
* This requirement covers most installations
For gas vents 12 inches in size or smaller, the vents may
terminate in accordance with the minimum heights listed in
Figure 43 provided they are at least 8 feet from a vertical
wall or similar obstruction. All other gas vents must
terminate not less than 2 feet higher than any portion of a
building within 10 feet.
From the looks of your install, your vertical vent should've been more than 8' from a vertical wall and would have only required 4' above the roof penetration. What requirements were your inspectors quoting?