Member
Hello,
I've been dealing with a back drafting issue with both my gas water heater (year round) and boiler (winter use only). The mechanical area they are in is tight, but is directly off a 9'x9' laundry room. In the laundry area I have an awning window (roughly 28" x 12") that i find myself having to crack open pretty much for the entire winter so my appliances down there exhaust correctly. We have two Co2 detectors in there (redundant) and they never alert. However, I can smell something in the air when either unit is running. On top of all that the door is kept wide open at all times.
I recently installed a 12"x6" vent on the lower portion of the bedroom wall that is adjacent to the water heater area. I tested the water heater and nothing changed. This past weekend I installed a 4" fresh air pipe on the side of my house which goes down into the mechanical area hoping to correct the problem, NOPE same thing happens... right away the WH started to backdraft. Cracking the window open in the room stopped the back draft. I double checked that the air pipe is bringing in air and you can very noticeably feel air flowing in (window closed and no exhaust vents running in house, clothes dryer is off). The room itself was built out from scratch by myself during our house reno. All cracks and seams in foundation and sill areas were sealed and or repaired. The foundation walls were sealed with 2 coats of dryloc, insulated with 1/2" foam board and all studded walls are insulated with r13 insulation. So there's not many places air can get in that area.
What am I missing here? Please help!
Here are some photos for reference showing the room in question with dimensions:



Both installed 2019:
-AO Smith 50 gallon Gas fired water heater
-Burnham ES25 - Gas fired boiler (1 base board zone and hydronic heating)
Summer Months - water heater only:
- water heater backdrafts
- causes a noticeable combustion smell in the area
- exhaust pipe is cold while its running
- cracking the window open slightly immediately causes the exhaust pipe to heat up and the smell goes away relatively quickly
Winter Months - Both are in use:
- Both the water heater and boiler backdraft with window closed and door kept wide open
- the boiler thermal switch will trip and noticeable smell in the room
- with window cracked, the exhaust pipe is hot and no smell
I've been dealing with a back drafting issue with both my gas water heater (year round) and boiler (winter use only). The mechanical area they are in is tight, but is directly off a 9'x9' laundry room. In the laundry area I have an awning window (roughly 28" x 12") that i find myself having to crack open pretty much for the entire winter so my appliances down there exhaust correctly. We have two Co2 detectors in there (redundant) and they never alert. However, I can smell something in the air when either unit is running. On top of all that the door is kept wide open at all times.
I recently installed a 12"x6" vent on the lower portion of the bedroom wall that is adjacent to the water heater area. I tested the water heater and nothing changed. This past weekend I installed a 4" fresh air pipe on the side of my house which goes down into the mechanical area hoping to correct the problem, NOPE same thing happens... right away the WH started to backdraft. Cracking the window open in the room stopped the back draft. I double checked that the air pipe is bringing in air and you can very noticeably feel air flowing in (window closed and no exhaust vents running in house, clothes dryer is off). The room itself was built out from scratch by myself during our house reno. All cracks and seams in foundation and sill areas were sealed and or repaired. The foundation walls were sealed with 2 coats of dryloc, insulated with 1/2" foam board and all studded walls are insulated with r13 insulation. So there's not many places air can get in that area.
What am I missing here? Please help!
Here are some photos for reference showing the room in question with dimensions:



Both installed 2019:
-AO Smith 50 gallon Gas fired water heater
-Burnham ES25 - Gas fired boiler (1 base board zone and hydronic heating)
Summer Months - water heater only:
- water heater backdrafts
- causes a noticeable combustion smell in the area
- exhaust pipe is cold while its running
- cracking the window open slightly immediately causes the exhaust pipe to heat up and the smell goes away relatively quickly
Winter Months - Both are in use:
- Both the water heater and boiler backdraft with window closed and door kept wide open
- the boiler thermal switch will trip and noticeable smell in the room
- with window cracked, the exhaust pipe is hot and no smell
Attachments