Back Feeding With A Generator

dledinger

Well-known member
Joined
Apr 14, 2009
Messages
345
Very nice work. BTW, I think the wetstacking problems with the 800 series generators are greatly exaggerated. Most of the ones I have seen had been run A LOT with zero load to get to that point - like running weekly to keep the batteries charged with no load, or powering a tent with 3 60 watt lamps and running nonstop for 2 months. Put a good load on them for an hour and they clear right up. I've spent counteless hours with my head inside of the TQGs 10-60kw) and I wouldn't hesitate for a second to buy one.
 
To avoid these ads, REGISTER NOW!

95blklsc

Well-known member
Joined
Dec 11, 2009
Messages
45
Excellent info, thanks. While I would love a TQG, I totally don't need it...but I still want one...
 

RonRock

Well-known member
Joined
Oct 6, 2007
Messages
1,171
Location
Iowa, USA
So I'm planning on using an interlock kit for my emergency generator. I've been convinced it is a better way to go than backfeeding through my welder plug. I've done some searching and have seen breakers that are red handle. I assume that is an obvious way of marking them as "special purpose." Are they actually different than any other double pole breaker? Where to buy them if they are special?

When power goes out, what is best practice for powering up with the genny? I understand the interlock portion, my question is as far as power use on startup. Say I have a 5,000 watt generator, power goes out. Will the generator start and run enough for me to "lighten the load" or is it best to drop all of the breakers then power up as needed? House is LPG, so no heavy loads other than HVAC which could easily be turned off when in AC mode.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Only red handle breakers I've seen are old Bryant breakers,and it's best to turn all breakers off and then turn them on one at a time
 

Hpozzuoli

Well-known member
Joined
Dec 11, 2013
Messages
3,428
Location
Rhode Island
No fancy colors for the breakers. When the power goes start the gen and let it run for a few mins. When warmed up plug into house with all breakers off. Start opening each breaker one at a time till you have everything on that you need.

Do not start the gen and immediately dump the whole house on it.
 

Attachments

  • image.jpg
    image.jpg
    69 KB · Views: 25

Hpozzuoli

Well-known member
Joined
Dec 11, 2013
Messages
3,428
Location
Rhode Island
You want a regular gen plug running into your panel. My house is all natural gas. My electrical draw is small compared to what most will need. I have a 10hp diesel that runs 6500/6000. More than enough for what my house requires. I have (2) two ton ad units that I don't even bother to try and run cause I can't.
 

Attachments

  • image.jpg
    image.jpg
    57.4 KB · Views: 18
To avoid these ads, REGISTER NOW!

RonRock

Well-known member
Joined
Oct 6, 2007
Messages
1,171
Location
Iowa, USA
Cool thanks guys. Looks like a normal breaker it is. Makes sense to start the generator first, then go to panel and shut down everything. Then switch from main breaker to generator. Then switch on necessary breakers.

I'll have to do a test run and make notes. Then a sticker with the procedure for my wife.


As a side note. Anyone have experience with the Generlink?

http://generlink.com/about_generlink.cfm

Looks like a good way to go with a bigger generator than mine. Not sure if it is available in my area, and they don't show a price.
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
As a side note. Anyone have experience with the Generlink?

http://generlink.com/about_generlink.cfm

Looks like a good way to go with a bigger generator than mine. Not sure if it is available in my area, and they don't show a price.

That looks like a cool concept and easiest for someone that wants to have a backup generator but without doing any rewiring.

Probably best to call your local power company first and ask them about it. Anything involving the meter / meter can they can be touchy about.
 

sparelman

Member
Joined
Aug 23, 2012
Messages
9
Location
Virginia
What do homeowners, who are feeding the grid with solar power, do when the power goes out? Do they have a switch that disconnects their power source?

If I were a lineman, with the availability of I power sources today (solar, wind, generators, etc), I'd check, double check and then still treat that line like it was live. I'm not justifying back feeding a generator, I just wouldn't trust people these days considering how accessible things are now.

FWIW - I didn't see a response for this, so thought I'd mention it. Typically the inverters used in solar applications have an automatic switch.

The inverters for my solar system (a non battery backup system) need to see the proper frequency of the electricity coming in from the power company before they will switch on and feed power from the solar array. In a power outage they will automatically disconnect.

This was checked by the power company, by pulling our meter ( disconnecting us from the grid) and observing the inverters - before they would certify and allow our unit to be commissioned into service.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,751
Homes built since 1996 have had 4 wire dryer receptacles mandated by the NEC. Therefore they have a neutral included. Some jurisdictions may not have enacted it right then. But it's definitely the rule everywhere by now. 3 wire might still be around in older homes. But any newer dryer than 2000 model, will require a neutral to have 125/250v, for electronics, etc. Hence the 4th wire.

A transfer switch is the best option. An interlock with an inlet and cord would probably be second best.

"Knowing to pull meter or turning off the main to avoid back feeding the utility" is waaaaay down the list of preferred methods.

You have a misunderstanding of dryer/ range receptacles, the 3 wire ones are dual voltage 125/250V NON-grounding devices which means there is a neutral and no grounding conductor, as it was permitted to ground the frame of the appliance to the grounded(neutral) conductor. The 4-wire receptacle means the grounded & grounding conductor are seperate as they should be.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757