I was told that I should use backer rod in my control joints prior to filling them.

The issue is my joints are .090-.095 in width. The smallest diameter backer rod I could fine was .250. I tried getting that in the saw cut and that would be a mother to put in 600 ft.

Two questions:

Is using backer rod absolutely necessary?

Do they make backer rod in a smaller diameter than .250.
I have searched and could not find any.

Thanks
 
To avoid these ads, REGISTER NOW!

7th Kahuna

Well-known member
Joined
Aug 4, 2012
Messages
1,704
Location
Los Angeles, CA
In my experience the backer rod has always been used in larger joints to limit the amount of filler required while at the same time assuring a solid and consistent fill near the surface. If your joints are that tight, I don't see the need. I am assuming this is a flat rather than vertical surface. If the depth of the cut is such that you don't believe you will get a consistent seal, perhaps you could 'back-fill' with a bit of fine silica sand first, brushed out to a relatively consistent depth, and then seal the joints. Just a thought.
 

EJM02

Well-known member
Joined
Oct 23, 2011
Messages
149
Pics help. There may be another approach you can try but hard to tell without seeing the issue.
 

bigman68

Well-known member
Joined
Mar 7, 2012
Messages
173
Location
N.E. Indiana
You should always use backer rod in a joint you are going to caulk. An ideal caulk depth is 1/2 of it's depth with a max of about 1/2" thick. Think of it this way... I will use the rubber band theory... RUbber bands are thin and that let's them stretch, if they were equal on all sides like a chunk of rubber it would not stretch, a control joint is cut in concrete to control where concrete cracks, the caulk put in must stretch as the concrete moves, if it is thin like a rubber band it will stretch and not pull away from the sides of the joint, if you pour it at full depth, like a chunk of rubber it will not stretch, and it pull away from the side of the joint. The smallest backer rod available is 3/8" which is used for your standard saw cut, look in your yellow pages under " Concrete Accessories" you will find supply houses that sell this size, we sell 3/8" up thru 6". Also ask for a Backer Rod Insertion Tool like this:

http://www.albioneng.com/home/produ...d_and_Corner_Model_Backer_Rod_Insertion_Tools

It will make your life way easier for around $50.00.
 
To avoid these ads, REGISTER NOW!
OP
D

dieselgarage

Well-known member
Joined
Dec 18, 2012
Messages
277
Thanks for the replies. Give me some new things to consider. I have a roll of .250 backer but with out some serious squeezing and squishing it will not go in the saw cut.

Might have to look into the sand idea.
 

Always_Thinkin

Well-known member
Joined
Aug 14, 2012
Messages
300
Location
Illinois
You don't need backer rod for control joints only for expansion joints. I deal with this on a large basis with concrete floodwalls and closure structures.
 