Kevin54
MEMBER EMERITUS
Ran into an electrical problem in the garage yesterday. I was checking out a furnace blower motor and squirrel cage. I just peeled the wires and stuck them into the end of an extension cord to see if the motor was good. I got an arc but never popped a breaker. I then noticed the clock plugged into that same circuit was out. With checking with a plug in electrical checker it showed an open neutral, so I started checking other outlets on the same circuit all on one wall. I started changing out outlets one at a time
I kind of remember wiring the garage and did have some help so I wasn't sure where everything was exactly at. I replaced five outlets that showed an open neutral. On the sixth which I did not see right off was back behind my toolbox, I pulled it, everything looked good EXCEPT this one particular outlet was backstabbed for some reason. I swapped it out and everything was back in working order.
Now that brings up a question. I pulled the cover off of the panel box when I was part way through changing outlets. I noticed that the neutral for that particular bank of outlets had two neutrals in on spot, so I moved it to a blank spot. In doing so (no I didn't kill the breaker), the neutral his the box side. The neutral was hot. I checked with my electrical meter and I was getting something like 117 volts through the neutral
So my question is, why did it not pop the breaker if it was shorted in an outlet? Mind you the outlet looked to be still in great shape, nothing charred, just that it was a backstabbed outlet.
I am also very thankful that the garage did not burn down. I guess with nothing plugged into the outlets AFTER the bad outlet is what save it. So I now have the task of going around and seeing if I have any other outlets that have been backstabbed. I guess when you have help doing something, never take for granted that just because they say they know what they are doing, that they actually do. I know that you are allowed to backstab but I don't like to do it jusdt for the fact that I have seen wires pull back out.
I kind of remember wiring the garage and did have some help so I wasn't sure where everything was exactly at. I replaced five outlets that showed an open neutral. On the sixth which I did not see right off was back behind my toolbox, I pulled it, everything looked good EXCEPT this one particular outlet was backstabbed for some reason. I swapped it out and everything was back in working order.Now that brings up a question. I pulled the cover off of the panel box when I was part way through changing outlets. I noticed that the neutral for that particular bank of outlets had two neutrals in on spot, so I moved it to a blank spot. In doing so (no I didn't kill the breaker), the neutral his the box side. The neutral was hot. I checked with my electrical meter and I was getting something like 117 volts through the neutral
So my question is, why did it not pop the breaker if it was shorted in an outlet? Mind you the outlet looked to be still in great shape, nothing charred, just that it was a backstabbed outlet. I am also very thankful that the garage did not burn down. I guess with nothing plugged into the outlets AFTER the bad outlet is what save it. So I now have the task of going around and seeing if I have any other outlets that have been backstabbed. I guess when you have help doing something, never take for granted that just because they say they know what they are doing, that they actually do. I know that you are allowed to backstab but I don't like to do it jusdt for the fact that I have seen wires pull back out.