TractorJeff
Well-known member
PS
Static pressure of 11 inches isn't the same as flow pressure of 10 inches. There maybe a flow restriction in the line.
Also
I don't believe that is a copper thermocouple line but a pressure tube that senses flame/heat thus allowing the Gas valve to open. If it is damaged/crimped you may not be getting the "Its Safe to Flow Gas" signal the Gas valve requires!
For what its worth!
In my attic is an old early 80's vintage propane furnace re-jetted for natural gas. The Tech shows up to service the new TRANE downstairs. Looks at his work order sheet that says check and adjust gas pressure of upstairs furnace. He goes up there, sees the vintage, gets angry/salty. He insists you can't run a propane furnace on natural gas! I tell him I am sure it has been re-jetted in its lifetime or it would have failed by now. I threaten to call his Boss if he doesn't do as WO states. He knuckles under, checks it, adjusts a little as it was slightly low.
Moral of the story is;
GOOGLE is your friend! Ask for opinions and suggestions here! Study your Unit and compare to other old furnaces.
Not every Furnace Tech can handle OLD units!
Static pressure of 11 inches isn't the same as flow pressure of 10 inches. There maybe a flow restriction in the line.
Also
I don't believe that is a copper thermocouple line but a pressure tube that senses flame/heat thus allowing the Gas valve to open. If it is damaged/crimped you may not be getting the "Its Safe to Flow Gas" signal the Gas valve requires!
For what its worth!
In my attic is an old early 80's vintage propane furnace re-jetted for natural gas. The Tech shows up to service the new TRANE downstairs. Looks at his work order sheet that says check and adjust gas pressure of upstairs furnace. He goes up there, sees the vintage, gets angry/salty. He insists you can't run a propane furnace on natural gas! I tell him I am sure it has been re-jetted in its lifetime or it would have failed by now. I threaten to call his Boss if he doesn't do as WO states. He knuckles under, checks it, adjusts a little as it was slightly low.
Moral of the story is;
GOOGLE is your friend! Ask for opinions and suggestions here! Study your Unit and compare to other old furnaces.
Not every Furnace Tech can handle OLD units!
. Here's a picture of the offending pipe dope. Thanks again for everyone's suggestions and help.
In the end, it would have still cost me the same amount of money, as all of the issues I had to pay for were due to my installation techniques. It did cost me several hours of work to fix the old beast, but that's cheap compared to the $1500+ for a new furnace. Score a big one for the cheapstake.