I've gotten pretty heavily involved with rehabbing a local baseball field for the boys.
Money is limited, so we are trying to what we can as funds are available.
Having said that, I have managed to scavenge some older 1500W metal halide field lights. The plan is to install 4 of these on 4 poles around the field with the intentions of upgrading to LED's when the next batch of funding is available.
So for now we are installing a new service, new poles, conduit, wire, and old lights.
I am trying to put together an estimate for this work and have 2 options:
Option 1:
Install service on the press box (370' from nearest transformer) with breaker panel. Power company will require 400 amp meter base to reduce voltage drop using larger wire size. Service will still be a 200 amp service. I am responsible for underground conduit and meterbase.
Then run 250' from the farthest pole back to meter base. At 1500W x 4 ea. / 240v x 1.25, that is roughly 32 amps. Is No. 6 THHN sufficient for this?

Option 2:
Place service on Light Pole nearest transformer with breaker panel. (170' away) Can use 200 amp meter base. Then run circuits, 150', 250', 400' to the other 3 poles. Again is No. 6 THHN sufficient for these runs?

I like option 2 the best for cost reduction of conduit, BUT if the wire size needs to increase, it may offset any savings.
Any suggestions?
Money is limited, so we are trying to what we can as funds are available.
Having said that, I have managed to scavenge some older 1500W metal halide field lights. The plan is to install 4 of these on 4 poles around the field with the intentions of upgrading to LED's when the next batch of funding is available.
So for now we are installing a new service, new poles, conduit, wire, and old lights.
I am trying to put together an estimate for this work and have 2 options:
Option 1:
Install service on the press box (370' from nearest transformer) with breaker panel. Power company will require 400 amp meter base to reduce voltage drop using larger wire size. Service will still be a 200 amp service. I am responsible for underground conduit and meterbase.
Then run 250' from the farthest pole back to meter base. At 1500W x 4 ea. / 240v x 1.25, that is roughly 32 amps. Is No. 6 THHN sufficient for this?

Option 2:
Place service on Light Pole nearest transformer with breaker panel. (170' away) Can use 200 amp meter base. Then run circuits, 150', 250', 400' to the other 3 poles. Again is No. 6 THHN sufficient for these runs?

I like option 2 the best for cost reduction of conduit, BUT if the wire size needs to increase, it may offset any savings.
Any suggestions?