Baseboard Thermostat self heating?

couch67

Well-known member
Joined
Mar 18, 2016
Messages
1,430
Location
Ontario Canada
I ended up replacing a 2 pole thermostat in the garage that had failed (20 yrs old, contacts were sticking). Replaced with a Dimplex 2 pole, rating at 240v is 5200 watts. Its controlling 3 baseboards totaling 4000 watts.

What I'm seeing is the thermostat setpoint needs to be turned up quite a bit higher to get the temperature I want. Say to get the garage to 15C (60F), I need to set the t-stat to 22C (72F).

While double checking all my connections are tight, I noticed the inside of the box was warm, measured about 72F with an infrared thermometer. Its on a shared wall to the house (2x4 insulated), so I thought it could be heat from the house. So I turned off the heat in the garage for 30 min, taped off the hole and then measured the temperature in the cavity. It was back down to the garage temp, more or less.

Next thing I checked is the thermostat self-heating? Well, when its on and supplying power to the baseboards, The wires supplying the thermostat do get warmer - about 72F. Its 12-2 NMD90 throughout, and not a long run to the panel - about 20 feet. Current at the panel is 16 Amps, which jives with the baseboard wattage.

I know there would be a slight raise in wire temperature with 16 Amps, but was surprised this much. Anyone run into this before, and would this be considered normal for a t-stat installation? Turning the setpoint higher isnt a big deal, but just checking if I'm overlooking something unsafe.
 

Attachments

  • Image00006.jpg
    Image00006.jpg
    43.5 KB · Views: 29
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

David0858

Well-known member
Joined
Oct 30, 2016
Messages
201
Location
Tx
I've had line level baseboard thermostats do that. Actually, all the manual thermostats have done that to a greater or lesser degree. The electronic ones I have now don't seem to have that problem.
 
OP
C

couch67

Well-known member
Joined
Mar 18, 2016
Messages
1,430
Location
Ontario Canada
Thanks for the replies. Wylies, no circuit board that is visible, its a metal body and the back is plastic/resin, and doesn't appear to be serviceable.

There is a metal tab to the right of the temperature dial, and it has an adjustment that is factory thread sealed. Assuming that is the temperature calibration. Likely wont fuss with it, just glad its not a safety concern.

One day I might go to electronic, one day....
 

Attachments

  • 20210121_194058 (2).jpg
    20210121_194058 (2).jpg
    73.4 KB · Views: 7