John...sorry if I wasn't clear. If the anchors are popping, it can be from a few different issues. 1.) the anchors are pulling out 2.) the concrete isn't strong enough to hold them in or 3.) the lift is not level (he said he has a sloped floor) or shimmed properly
1a) The anchors weren't torqued correctly
1b) The anchors are poor quality
2a) This would be evident by spalling / damaged concrete
3a) Level is insignificant, within reason, in regard to anchor loading,
3b) Shimmiing is insignificant in regard to anchor loading. It can be significant in regard to concrete compressive stresses though.
Using epoxy anchors isn't going to solve the problem, in and off itself, if A.) the concrete isn't strong enough or B.) The anchors are pulling out but he can't get them out completely. Pounding the existing anchors through the floor is usually a bad idea as well. That can or will cause a blowout on the underside of the concrete and he's borderline already if the mfg is calling for 6" and he only has 5.5".
Epoxy anchors can indeed fix the problem. Their mode of attachment provides less stress on the concrete and they therefore have superior performance. They don't "add" to the stress on the concrete the way mechanical anchors do.
To use epoxy anchors, he will need to core out the existing anchor holes to a larger diameter. The epoxy needs approximately 1/8" minimum around the new anchor in order to get a good grip. If he's going to core out all the anchors (or drill them out), it would probably be easier to cut the floor and pour a new pad. At least he could pour it level without the other column and the amount of work is going to be about the same!
Cutting concrete out and replacing it is easier than drilling out a few holes?
He can drill out the holes without even moving the lift.
If the concrete is the problem (soft & silty, poor psi strength, etc.), the epoxy won't make it any better. The anchors will stay glued to the concrete, but the concrete may still crumble and come up around the epoxy.
Agreed
If it's only 1 or 2 anchors coming loose, I could see drilling them out (or coring them out) and replacing with epoxy, but he really didn't say if they were ALL coming loose or just a few of them.
Cdmartin stated:
Floor thickness specifies 6 inches. I drilled 1 hole and it was every bit of 6 inches. So I installed one post with no issues. Once I n got to the other side, the floor slopes to a drain and the concrete on that side is closer to 5.5" where the outside lift anchors are. That's where they are trying to pull out. ...
"The base will try and pull out of the floor" should have been "the base will try and pull the anchors out of the floor". My bad on that...If the base is not level and you are lifting a vehicle on the lift, the base acts as a lever (fulcrum), pulling the anchors out.
The base always acts as a lever, the lift being out of level will make a negligible difference, if any.