Bathroom lights over sink: GFCI or not?

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
In-laws house is a 1960s and existing wiring to the upstairs bath has no GFCI anywhere. There’s a combo switch-single-receptacle that controls the lights over the sink and provides a single outlet. (No fan in the room.) That circuit *is* shared with several other rooms as well.

What I intend to do is to replace the combo with a normal switch and cut a new box into the wall at calf height and put a GFCI outlet there as that would be safer than the current (no pun intended) arrangement.

My question is: should I wire the lights on the load side of the GFCI (take a 12/3 down the wall) or leave the lights off the GFCI?

(Rewiring to isolate the bath or adding a fan is off the table at this point.)
 
To avoid these ads, REGISTER NOW!
OP
S

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Wow. Never even thought that a GFCI-switch combo would exist. That’s surely the easiest and good enough option.
 

MeentSS02

Well-known member
Joined
Aug 12, 2010
Messages
325
Location
Dayton, OH
Where would a GFCI protected lighting fixture be required? Any time I've ever tripped a GFCI, it's been because I've been doing something I shouldn't have been doing...if the lights had also gone out at the same time, that probably would have only made things worse.

It's certainly not a bad idea on paper, but I can't figure out if it passes the common sense test.
 
OP
S

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Only thing I’m (only very slightly) worried about is touching the plumbing while changing a light bulb and taking a shock instead of darkness.

I’m leaning against, but figured I’d use the wisdom of GJ crowd.
 

MeentSS02

Well-known member
Joined
Aug 12, 2010
Messages
325
Location
Dayton, OH
Only thing I’m (only very slightly) worried about is touching the plumbing while changing a light bulb and taking a shock instead of darkness.

I’m leaning against, but figured I’d use the wisdom of GJ crowd.

I could see that.

I'm genuinely curious...my house was built in the late 80s, and none of the lights in my bathrooms, kitchen, or laundry room where GFCIs reside are protected. Same for my garage. Just wondering if there was a recent code change, or if it was just considered a best practice.
 

Greeny

Well-known member
Joined
Feb 25, 2013
Messages
572
Location
Shreveport, LA
My 1986 home has the lights on the same circuits as the GFCI outlets. Pop an outlet and the lights are out as well.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Lights are not required to be on GFCI. If you do your plan of putting in a GFCI lower on the wall (not sure I'd do this as it's a strange arrangement for a bathroom to have an outlet mounted at that height) and are going to protect the lights too, you can't run a 12/3 as you suggested to it to make it work. It would need 2 runs of 12/2 as the neutrals have to be separate.

I would either enlarge the existing box to a 2-gang and install a regular switch and GFCI, no protection for lights, or install a second 1-gang cut-in box next to the existing switch with the same arrangement.
 
To avoid these ads, REGISTER NOW!
OP
S

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Good catch; thanks!

Now I’m doubly glad I asked here rather than just diving in and having the GFCI probably trip every time I hit the lights and then not protecting them anyway...
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,179
Location
Chicago, IL
My question is: should I wire the lights on the load side of the GFCI (take a 12/3 down the wall) or leave the lights off the GFCI?

No. GFCI's trip from the appliances all the time. The last thing you want is a bad shaver to trip the GFCI and then also have it cut out your lights at the same time.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,977
Where would a GFCI protected lighting fixture be required?

They're required on 120V lighting outlets (which is NEC for "light fixtures") in crawlspaces as of the 2017 code cycle. That's the only place I know of.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,354
Location
Alexandria, VA
I saw a post in another forum that said the 2020 NEC revision added a requirement for GFCI lighting fixtures in garages, but I've never seen the actual reference. It will also be quite a while before any AHJ adopts the 2020 code.

Bruce
 

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,461
Location
Colorado
Be aware that adding light circuits to GFCI can false trip if you switch to some LED bulbs, just as your TV and FM radio reception can go south. RF interference.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
They're required on 120V lighting outlets (which is NEC for "light fixtures") in crawlspaces as of the 2017 code cycle. That's the only place I know of.
They're also required for light fixtures (and ceiling fans) located within 10 ft horizontally of a swimming pool, hot tub, or fountain.

I saw a post in another forum that said the 2020 NEC revision added a requirement for GFCI lighting fixtures in garages, but I've never seen the actual reference. It will also be quite a while before any AHJ adopts the 2020 code.

Bruce

I've read the 2020 NEC (and you can too here: https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70 ). There is nothing in there that says lighting fixtures in garages need GFCI.
 