Beacon morris bru 45 garage heater

adtinner12

Member
Joined
Apr 27, 2024
Messages
5
I have an older unit I was given in exchange for some work it’s currently running off of LP. Everything works great but for the some reason the fan is always blowing, even after hitting the desired temp everything else will turn off but the fan will continue to run. I’ve had it on for several hours and it will cycle to maintain temp but as long as the unit has power that fan is always on. Any ideas on a solution???
 
To avoid these ads, REGISTER NOW!

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
352
Location
SE IA
Is there a "G" terminal on the control board? If so, did someone put a jumper on it?
 
To avoid these ads, REGISTER NOW!
OP
A

adtinner12

Member
Joined
Apr 27, 2024
Messages
5
Thanks! Troubleshooting says it must be a wiring issue on the control board so I’m going to try that route.
 
OP
A

adtinner12

Member
Joined
Apr 27, 2024
Messages
5
Found the issue the one wire off of m2 blower was not connected to acc1 on control board works perfectly now the board is wired properly
 