I have a nat. gas heater in my shop. Lately, it lights and heats up, but the fan only comes on about 1/2 speed for about 5 seconds then shuts off. Any ideas?
I checked. It flashes 4 times. It say's that the limit or rollout switch maybe open, however, I can't find one on this unit. This is a 150000 BTU unit, Model TF/BTU150
The power vent fan runs constantly, the blower fan comes on and runs for about 5 seconds, then shuts off, then, the ignitor clicks and the gas lights and stays on for about 10-15 seconds, then goes out. Then it starts all over again. I watched this today.
^^^^^^^^^^That explanation sounds more like the flame sensor is not being satisfied.
The flame sensor confirms a flame is lite and present. If not satisfied it shuts down the gas valve. Then starts lol over again. Most units give up after 3-5 try’s. The flame sensor generate a few micro amps so they are very sensitive to dirt or corrosion.
Often they are just dirty and cleaning is all that is needed witha dollar bill or scotch Brite pad.