I have a nat. gas heater in my shop. Lately, it lights and heats up, but the fan only comes on about 1/2 speed for about 5 seconds then shuts off. Any ideas?
 
To avoid these ads, REGISTER NOW!
OP
M

MountNMan56

Member
Joined
Feb 6, 2019
Messages
11
Location
Heath, Ohio
I checked. It flashes 4 times. It say's that the limit or rollout switch maybe open, however, I can't find one on this unit. This is a 150000 BTU unit, Model TF/BTU150
 
To avoid these ads, REGISTER NOW!

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
You mentioned the fan blower was running half speed????

If that’s the exhaust power vent running slow..........then the roll out sensors would sense an over heat situation.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Slow main fan could also cause an overheat situation tripping the safety sensor.

The tripping has a cause and resetting then detailed testing is critical.
 
OP
M

MountNMan56

Member
Joined
Feb 6, 2019
Messages
11
Location
Heath, Ohio
The power vent fan runs constantly, the blower fan comes on and runs for about 5 seconds, then shuts off, then, the ignitor clicks and the gas lights and stays on for about 10-15 seconds, then goes out. Then it starts all over again. I watched this today.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
^^^^^^^^^^That explanation sounds more like the flame sensor is not being satisfied.

The flame sensor confirms a flame is lite and present. If not satisfied it shuts down the gas valve. Then starts lol over again. Most units give up after 3-5 try’s. The flame sensor generate a few micro amps so they are very sensitive to dirt or corrosion.

Often they are just dirty and cleaning is all that is needed witha dollar bill or scotch Brite pad.
 