Fuel oil furnace is acting up, it works fine for a cycle then it doesn't try to light. It brings the house temp up to the setting and shuts off normally, when it is time to start again it doesn't even try to start and the blower motor comes on immediately. If I kill the power to it for 30-45 minutes, it starts right up normally and runs a normal cycle, then won't start again. Any help with a place to start troubleshooting would be greatly appreciated, the manual that came with it is no help.

Very few guys around here will work on oil furnaces and they seem to be too busy to return a phone call.
Thanks
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,510
Location
The UP, God's country
Flame detector is where I would start. I previously had an oil boiler in the shop and that was the number one issue.

Ditched it and went propane because all the old guys that worked on oil were rapidly retiring and there was hardly anyone left willing to work on the oil burners.
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,288
Location
Southeastern Pa
Since it does not even try to start the igniter is where I would start, check the flame sensor only if it's igniting and than shutting down

 
OP
M

Mike in Ohio

Well-known member
Joined
Sep 27, 2008
Messages
2,415
Location
Canton,Ohio
It seems like when I kill the power something resets. When I say doesn't try to start I mean it is like the burner is not being told to. no pump running, no lights on the burner, just the blower at the other end starting, it isn't supposed to come on till the burner has light for 30 seconds. When I turn the power on the pump starts immediately and it lights a few seconds later and runs normally. I will check the things mentioned though.

Thanks
 

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,439
Location
Indiana
When was the last time it was serviced? Nozzle replacement, igniters adjusted replaced. air inlet cleaned adjusted. etc.

i have one they don't run on autopilot forever. ( I tried)

Maybe something is getting too hot.
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,353
Location
Hunterdon County NJ
Sounds like the high limit switch maybe is acting up because it will start the burner after a 30-45 minute cool down…….. IMHO the burner is not the problem.
A professional burner service is highly recommended…….. New oil filter, clean the cad cell, check draft along with servicing the chimney and test for efficiency.
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,837
Location
Fargo, ND
That is odd. Usually the cad cell never sees flame when they fail. I suspect you had another issue that you accidentally fixed when you had it a part.

Years ago I worked on a lot of oil. I was the "oil guy" at our shop.
 

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
3,041
Location
Northern Wi.
Me too. First thing I always did was new nozzle. Then yo can check all the measurements on the electrodes and wipe off the cad cell.

Oil can be finnicky and if it's old it probably needs to be cleaned. Depending on model and age this is one of those jobs americans won't do.

Your vacuum cleaner will never be the same and you will be very dirty. I made several adapter hoses so I could run 3/4 and 1 in. greenfield down into the second part of the heat exchanger and rattle it around for a couple hours.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,013
Location
Peace Valley,mo
No power was cycled, burner motor doesn't run but furnace blower runs. Correct? Furnace compleate model #, brand and picture of the wiring diagram if you have one. Check on back side of blower door. Have a volt meter?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
No power was cycled, burner motor doesn't run but furnace blower runs. Correct? Furnace compleate model #, brand and picture of the wiring diagram if you have one. Check on back side of blower door. Have a volt meter?

Read post #10
 
OP
M

Mike in Ohio

Well-known member
Joined
Sep 27, 2008
Messages
2,415
Location
Canton,Ohio
Let me try to explain better, I am not an hvac guy so bear with me. The cad cell kept "seeing" the flame after it had shut off. There is a little green light on the controller that comes on when it sees the flame ignite. That light did not go out when the flame shut off. Reset was probably the wrong word to use. But killing the power allowed it to quit "seeing" the old flame and "see" the new one.furnace control.jpg
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,837
Location
Fargo, ND
Let me try to explain better, I am not an hvac guy so bear with me. The cad cell kept "seeing" the flame after it had shut off. There is a little green light on the controller that comes on when it sees the flame ignite. That light did not go out when the flame shut off. Reset was probably the wrong word to use. But killing the power allowed it to quit "seeing" the old flame and "see" the new one.furnace control.jpg
Ok, seems reasonable when the burner control says so. I can't say I have ever seen a cad cell fail that way.
 