scottmoyer
Well-known member
I had a high lift added to my garage last week to accommodate a lift. I started researching lifts and came to the conclusion that the BendPak HD-9 might be my best option. While doing research on them, I came to this forum and found many threads regarding the same questions I had.
I am leaning towards the "110V" (120V) unit as my garage is attached to my home and the builder didn't provide power for anything other than garage door openers and a single outlet shared with other rooms in the house. I have seen many posts where 15A service was mentioned as ok. I also saw some that said 20A was required and some that said 30A is recommended.
I called BendPak to get a final answer and was surprised at what I was told. The rep said that the standard 15A would work fine. I suggested that I heard a startup current could exceed 17A and that would trip the circuit. At that point, he said that a 20A would be fine, but 30A is preferred. I told him that I'd have to pull new wire from the panel to get the 30A. His suggestion was to just replace the breaker on the existing 15A line in the garage!
I questioned his liability on making a suggestion to people of installing a 30A breaker on 14-3 wire. He said it should be fine. I said it was fine until the wires overheat and burn the house down! At that point he said he'll look into that and get back to me. Three days and waiting.
Just for the record, anybody adding wiring for their lift, and using 120V/15A service, should consider using 20A. The plug is slightly different and the wire is 12awg, not 14awg.
If you do have it plugged into a standard 120V/15A service, have you had any issues with tripping the circuit?
I am leaning towards the "110V" (120V) unit as my garage is attached to my home and the builder didn't provide power for anything other than garage door openers and a single outlet shared with other rooms in the house. I have seen many posts where 15A service was mentioned as ok. I also saw some that said 20A was required and some that said 30A is recommended.
I called BendPak to get a final answer and was surprised at what I was told. The rep said that the standard 15A would work fine. I suggested that I heard a startup current could exceed 17A and that would trip the circuit. At that point, he said that a 20A would be fine, but 30A is preferred. I told him that I'd have to pull new wire from the panel to get the 30A. His suggestion was to just replace the breaker on the existing 15A line in the garage!
I questioned his liability on making a suggestion to people of installing a 30A breaker on 14-3 wire. He said it should be fine. I said it was fine until the wires overheat and burn the house down! At that point he said he'll look into that and get back to me. Three days and waiting.
Just for the record, anybody adding wiring for their lift, and using 120V/15A service, should consider using 20A. The plug is slightly different and the wire is 12awg, not 14awg.
If you do have it plugged into a standard 120V/15A service, have you had any issues with tripping the circuit?