His motor is rated SPL just like mine. Factory 6-20R cord plug.
There is deliberately no HP rating on the motor, otherwise the HP limit of the plug would apply.
SPL means nothing to the NEC. Its just an attempt to fool people into buying substandard ****. And it works apparently.
If it does not have horsepower listed on the nameplate, you would have to follow
430-6(A)(1)
"where the motor is marked in amperes, but not horsepower, the horsepower rating shall be
assumed to be the corresponding to the value given in Table 430-248"
According to the table the motor is over 2 hp.
Now if the cord and plug comes on the compressor from the factory wyliesdiesels in post 18 would be correct. Although I still wonder about the receptacle side motor hp being exceeded?
But you are suggesting that the OP use a plug that is not factory installed and isn't rated for the HP per NEC 430-6(A)(1) and the manufacture of an installed on cord 6-20P just because yours is.
That would be non code compliant advise.