Hi-

Long time lurker, first time poster.

I'm trying to run a feeder for a 100 amp subpanel from main panel in my basement to my attached garage (house built in a hill, so on the same level).

I've had two electricians out to take a look, and 3 potential approaches to doing this have come up:
1) Run a cable down a wall ~30 feet, enter the garage, and then run on the surface to subpanel in the garage ~15 feet (I'll be using conduit to run branches within the garage, so don't mind this cable on the surface; garage is cinderblock on 3 of 4 walls).
2) Run a cable down another wall (main panel in a corner) about 15 feet, then enter an I-beam soffit and run ~25 feet down that soffit, enter the garage, and then run ~20-25 feet to the subpanel.
3) Run through the ceiling ~35-40 feet to the subpanel.

Of these options, I favor 1 or 2. I'm going to repaint the basement walls anyway so I don't mind cutting a section out to run cable, but really don't want to mess with the textured ceiling.

Regardless of which one of those options I end up doing, or whether I do the work or hire an electrician (I'm getting estimates that look like 400-500 in labor, which I find a little more than I want to pay), the challenge is the wall. From what I can tell, the structure of the basement is cinder block with a 2x4 wall put on top to hold the drywall, except the 2x4's are turned sideways, so the actual amount of open space is ~1.5". Feeder cable for ~100 amp subpanel looks to be about 3/4" or bigger.

Any idea on the best way to approach this? About the best solution I have is to drill a 1" hole as centered as I can in each of the studs, and put metal protective plates on the front. I think this works from an NEC perspective (using metal covers where wire runs <1.5" from front of stud), and should be fine from a building code perspective since these walls aren't load bearing.

Any suggestions or thoughts would be helpful.

Thanks!
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
the cable for 100 amps is going to be a heck of alot bigger than 3/4.. (where did you get that from?)
cant run cable on the surface of the wall in the garage...has to be protected from physical damage.
 
To avoid these ads, REGISTER NOW!

trbomax

Well-known member
Joined
Mar 21, 2010
Messages
2,556
Location
starvation lake,mi.
I wouldn't even try to drill the hole.Just set your skill saw at 1 7/16" deep and remove 3/4" of the stud,then plate over it.That might not fly with mr inspector though. By the time you try to drill a 1" hole in the 2 by, theres not going to be any structure left anyway,and if the drill runs out,you have a mess that you have to chisel or end up sawing out anyway.
 

noslo04

Well-known member
Joined
Aug 20, 2009
Messages
68
Location
Northern Virginia
Would it be possible to go straight up from the basement through a finished wall on the first floor and enter the attic to run it over and then back down to the garage? That's what I did to run a #1 aluminum feeder for a subpanel in my attached garage.

A contractor friend suggested that I run it outside in conduit over to the garage, but I liked the way that I did it better.
 