I got my Mr Heater Big Maxx 50k heater installed and had an HVAC installer come out and verify my NG to LP conversion and make sure it was getting the proper flow through the valve. I believe he said for LP, we were looking for ~10.5" WC. However, with the adjustment screw maxed out, he was only able to get 9" WC.
He mentioned that I probably need a regulator coming off my LP tank, which didn't make much sense to me. My setup is (2) 100lb tanks, with this regulator: [can't post links apparently, regulator is MEGR-253H]
According to the specs (model is MEGR-253H), it is already set for 11" WC.
Plumbing out of the regulator is 3/8" immediately converted to 1/2" all the way to the heater. Could the 1/2" pipe be causing that much of a drop? My gas lines have been tested to 120psi air with a very soapy solution and no bubbles are present.
He mentioned that I probably need a regulator coming off my LP tank, which didn't make much sense to me. My setup is (2) 100lb tanks, with this regulator: [can't post links apparently, regulator is MEGR-253H]
According to the specs (model is MEGR-253H), it is already set for 11" WC.
Plumbing out of the regulator is 3/8" immediately converted to 1/2" all the way to the heater. Could the 1/2" pipe be causing that much of a drop? My gas lines have been tested to 120psi air with a very soapy solution and no bubbles are present.