I’m getting ready to run the wire for my Big Maxx heater install and I have a NEC code related question.
I started at section 422.12 it states.
Then I see that 210.63 requires a “service receptacle”
Does this mean that I need two circuits for this heater?
Since the furnace is 14 feet in the air does a disconnect need to be up there or can I use the circuit breaker for the disconnect?
I started at section 422.12 it states.
422.12 Central Heating Equipment. Central heating equipment other than fixed electric space-heating equipment shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump,
valve, humidifier, or electrostatic air cleaner directly asso-
ciated with the heating equipment, shall be permitted to be
connected to the same branch circuit.
Exception No. 2: Permanently connected air-conditioning
equipment shall be permitted to be connected to the same
branch circuit.
Then I see that 210.63 requires a “service receptacle”
210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
Does this mean that I need two circuits for this heater?
Since the furnace is 14 feet in the air does a disconnect need to be up there or can I use the circuit breaker for the disconnect?