Big Maxx Horizontal Vent Kit

Lantz

New member
Joined
Oct 24, 2010
Messages
3
I am hooking up my unit in Ontario and there is a door about two feet below where I want to put the exhaust exit. Is there a code issue with having the chimney over the door?

I rarely use the door if that matters.

My only other choice would be to go into the attic up a few feet and then through at the same point. I guess that I could also veer off at an angle to get it away from the door if it is still against code...but I really don't see it being an issue for a heater that will be used on occasion, but....

thanks
 
Last edited:
To avoid these ads, REGISTER NOW!

stealthbob

Active member
Joined
Jul 12, 2009
Messages
41
The book calls for:

"When horizontally vented, minimum clearance for termination
from any door, window, gravity air inlet, gas or electric meter,
regulators, and relief equipment is 4 ft."

Also if you are over a door you should also know that you have to watch the soffit:

Vent termination must be a minimum of 4' (1.2m) below or 4’
(1.2m) horizontally from any soffit vent or under-eave vent.

Along with living in Ontario I also have the same issue to deal with....question is do they mean diagonally for the door as well? They mention it for the soffit but not for the door.
 
To avoid these ads, REGISTER NOW!
OP
L

Lantz

New member
Joined
Oct 24, 2010
Messages
3
thanks, I was thinking that it would be an issue. Is this an issue that the gas guy would have or is it a building code? Fortunately, I don't have the soffit issue as its a raised ranch with a pretty empty wall. I may have to go through my garage ceiling to get some more movement, but may just get someone in to tell me what to do.

I just noticed that the 45K can vent using a 3" pipe but the kit converts to a 4". I may take the kit back and swap it down depending on what I decide to do.
 
Last edited:

babzog

Well-known member
Joined
Apr 20, 2009
Messages
2,117
Location
Eastern Ontario, Canada
It'll be a gas code issue that your installer will deal with. Whether or not there's also building code issues depends on whether or not you pulled a permit for the work... regardless, your gas guy will do the work to the code he's obliged to comply with and should affix a tag on the unit with his installation and certification information.

Went through this for a wall heater installation a couple of years ago while also changing (propane) suppliers. My gas guy knew more about the code than the gas company.
 