Black iron pipe working pressure?

To avoid these ads, REGISTER NOW!

twistedstang

Well-known member
Joined
Jan 13, 2016
Messages
274
Location
Lexington, MI
The pipe I'm not super worried about but what PSI can you run the fittings at?! :(

I'm building a liquid propane flame projector for a pyro music firework show. They want a 100ft+ height flame for at least 11 seconds, pretty tricky. They tried a bunch of commercial flame projectors but none of them could go that big.

I found a 33LB forklift propane tank dirt cheap. The stock liquid propane output valve has SUPER slow flow. So instead of using the stock valve I took out the pressure relief valve and put a tee where it screwed into the tank (3/4" NPT), screwed the pressure relief into the tee and put a 500psi rated stainless steel full port ball valve on the other tee port. All the flow you could ever want (run the tank upside down for liquid, right side up for vapor).

The scary part is liquid hammer :( There's a digitally controlled solenoid flow valve (on/off only, and it's pretty much instant) and with the ball valve fully open (running at full anger) I'd imagine there's going to be big liquid hammer when it closes!

They make a soft close solenoid valve but I wouldn't be able to use ONLY that valve as the flames dance to music for a bit before the big flame and need instant on/off for little fireball puffs. I think I could install BOTH valves (in series even) so during the music I can use my existing quick open/close valve, then during the full anger run I can lock the quick valve open and use the slow close valve to send up the big flame.

Another issue is the fittings get really cold when I run it at full anger. Does temperature effect how much pressure the fittings can take? I'm talking super cold like as in -44c/-47f. After the ice fell off the fittings the first time I used it they rusted almost instantly.

Where can you get beefier fittings? I found a shop selling stainless steel fittings and pipe but they said they are only rated to 150psi!?? They could special order me some 200psi rated ones but they wanted crazy cash for them.

The first time I ran it at full anger the ball valve cracked where the input threads are (on the high pressure/tank side). Luckily it wasn't a large leak and I was able to turn off the pilot light before it ignited. I had to vent all the gas out of the tank to replace the ball valve. I believe it cracked due to the huge amount of thrust from the liquid leaving the solenoid flow valve. It put angled pressure on the pipe and the ball valve is closest to where a pivot point would be so experienced a ton of bending force. I'll have to make sure I super support the solenoid flow valve and piping so no physical pressure is applied to the pipe/fittings.

Let me know where I can get beefier fittings if anywhere. Brass or stainless would be nice (to stop them from rusting instantly). Would like to avoid galvanized so no flakes make it into my control valves.

If my regulator ever fails we'll find out real quick! Nitrogen (3000psi) fed directly into the propane tank at 175psi (3/4" port from the nitrogen tank, 3/4" in/out port on the regulator, 3/4" jackhammer hose, 3/4" inch port directly into the forklift propane tank). Common practice in hot air ballooning (nitrogen injection).

And yeah yeah, I know, it violates the cert of the tank and probably a ton of other rules too.

LETS COOK!

-Jamie M.

You would want 3000# forged fittings. And yes, if the system could refrigerate, you want fittings and pipe that can handle it.
 
Joined
Nov 4, 2018
Messages
7
Location
Toronto, Ontario, Canada
You would want 3000# forged fittings. And yes, if the system could refrigerate, you want fittings and pipe that can handle it.
Oh baby, that's what I needed to know! McMmaster Carr has a bunch!

Thanks so much, ordering a bunch of sch 80 ******* and those high pressure fittings!

Any recommendations on what I should use for high pressure/low temp thread dope?

-Jamie M.
 
Joined
Nov 4, 2018
Messages
7
Location
Toronto, Ontario, Canada
Is it time to put this thread back to sleep before reviving it yet again in another 3 years?
No way, too much good info in here :)

jGD1ur.jpg


-Jamie M.
 

Gas Ax

Member
Joined
Aug 18, 2012
Messages
9
The pipe I'm not super worried about but what PSI can you run the fittings at?! :(

I'm building a liquid propane flame projector for a pyro music firework show. They want a 100ft+ height flame for at least 11 seconds, pretty tricky. They tried a bunch of commercial flame projectors but none of them could go that big.

I found a 33LB forklift propane tank dirt cheap. The stock liquid propane output valve has SUPER slow flow. So instead of using the stock valve I took out the pressure relief valve and put a tee where it screwed into the tank (3/4" NPT), screwed the pressure relief into the tee and put a 500psi rated stainless steel full port ball valve on the other tee port. All the flow you could ever want (run the tank upside down for liquid, right side up for vapor).

The scary part is liquid hammer :( There's a digitally controlled solenoid flow valve (on/off only, and it's pretty much instant) and with the ball valve fully open (running at full anger) I'd imagine there's going to be big liquid hammer when it closes!

They make a soft close solenoid valve but I wouldn't be able to use ONLY that valve as the flames dance to music for a bit before the big flame and need instant on/off for little fireball puffs. I think I could install BOTH valves (in series even) so during the music I can use my existing quick open/close valve, then during the full anger run I can lock the quick valve open and use the slow close valve to send up the big flame.

Another issue is the fittings get really cold when I run it at full anger. Does temperature effect how much pressure the fittings can take? I'm talking super cold like as in -44c/-47f. After the ice fell off the fittings the first time I used it they rusted almost instantly.

Where can you get beefier fittings? I found a shop selling stainless steel fittings and pipe but they said they are only rated to 150psi!?? They could special order me some 200psi rated ones but they wanted crazy cash for them.

The first time I ran it at full anger the ball valve cracked where the input threads are (on the high pressure/tank side). Luckily it wasn't a large leak and I was able to turn off the pilot light before it ignited. I had to vent all the gas out of the tank to replace the ball valve. I believe it cracked due to the huge amount of thrust from the liquid leaving the solenoid flow valve. It put angled pressure on the pipe and the ball valve is closest to where a pivot point would be so experienced a ton of bending force. I'll have to make sure I super support the solenoid flow valve and piping so no physical pressure is applied to the pipe/fittings.

Let me know where I can get beefier fittings if anywhere. Brass or stainless would be nice (to stop them from rusting instantly). Would like to avoid galvanized so no flakes make it into my control valves.

If my regulator ever fails we'll find out real quick! Nitrogen (3000psi) fed directly into the propane tank at 175psi (3/4" port from the nitrogen tank, 3/4" in/out port on the regulator, 3/4" jackhammer hose, 3/4" inch port directly into the forklift propane tank). Common practice in hot air ballooning (nitrogen injection).

And yeah yeah, I know, it violates the cert of the tank and probably a ton of other rules too.

LETS COOK!

-Jamie M.

I will put this as nicely as I can, but as you are talking about a "show" I can only assume you will be placing others at risk with this potential bomb you are building. From your post you clearly have no idea regarding even the base concepts of what you are talking about building. I would say step away from this project before you get your self, or more worryingly someone else killed.
 
Joined
Nov 4, 2018
Messages
7
Location
Toronto, Ontario, Canada
I will put this as nicely as I can, but as you are talking about a "show" I can only assume you will be placing others at risk with this potential bomb you are building. From your post you clearly have no idea regarding even the base concepts of what you are talking about building. I would say step away from this project before you get your self, or more worryingly someone else killed.
There's no "air" in the propane tank so technically it can't explode. It has a pressure relief valve even! The 3000psi from the nitrogen tank wouldn't even make it to the propane tank (if the regulator failed) before the rubber line would burst. I think the risk is pretty low of an explosion.

Because of the size of the fireworks involved there is a large distance between the crowd and any of the equipment. Everything is ignited remotely so even staff will be far away. The flame projector is the last thing in the show so no worries about it igniting anything else either.

A member here sent me an awesome PM with some new design ideas to keep the propane tank far away from the flame using soft lines to run to the flame tube, and that will stop any issues of physical pushing on the ball valve/pipes etc. Should be a much more reliable and safer design. Can't wait to test it.

-Jamie M.
 
To avoid these ads, REGISTER NOW!

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
I wouldn't want to be around that installation for too long. :eyecrazy:

Tommy

It was just testing short pieces threaded into valves. When the patch was slow we went through a huge pile of pipe and fittings that were torn out. We buffed and cleaned all the ******* and fixed all the valves. We pressure tested all the valves and even took 3 and 4" plug valves to 2000 psi(rated to 50 for load lines) just to see. Young and silly.
 

gearhead1

Well-known member
Joined
Oct 14, 2013
Messages
1,935
Location
NC
HD rated theirs lower because they don’t trust China.

Seriously, I’d try to find something US made. Guys where I used to work used steel hydraulic tubing because they could get it cheaper than the black pipe. If it holds 3000 psi of hydraulic pressure, it’ll hold 150 psi of air.
 

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
HD rated theirs lower because they don’t trust China.

Seriously, I’d try to find something US made. Guys where I used to work used steel hydraulic tubing because they could get it cheaper than the black pipe. If it holds 3000 psi of hydraulic pressure, it’ll hold 150 psi of air.

Working in the oilfield I can confirm that the oilfield pipe from China has definitely been found inferior.
 

Gas Ax

Member
Joined
Aug 18, 2012
Messages
9
There's no "air" in the propane tank so technically it can't explode. It has a pressure relief valve even! The 3000psi from the nitrogen tank wouldn't even make it to the propane tank (if the regulator failed) before the rubber line would burst. I think the risk is pretty low of an explosion.

Because of the size of the fireworks involved there is a large distance between the crowd and any of the equipment. Everything is ignited remotely so even staff will be far away. The flame projector is the last thing in the show so no worries about it igniting anything else either.

A member here sent me an awesome PM with some new design ideas to keep the propane tank far away from the flame using soft lines to run to the flame tube, and that will stop any issues of physical pushing on the ball valve/pipes etc. Should be a much more reliable and safer design. Can't wait to test it.

-Jamie M.

OK have fun :evil:

https://imgur.com/gallery/a3HQS0Q

^^^Really wish there was a way to directly embed video
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Perspective: PCP pellet air rifle is at 3000-4000 psi done with hand pump. So 150-200 psi black pipe air line seems like no big deal.

560D29B5-8EFC-407B-9346-3427F5791199.jpg
 
Joined
Nov 4, 2018
Messages
7
Location
Toronto, Ontario, Canada
Perspective: PCP pellet air rifle is at 3000-4000 psi done with hand pump. So 150-200 psi black pipe air line seems like no big deal.
I'm going to be running this 300 psi hose, rated down to -40f, from the propane tank to the flame tube (should have 175psi in it): https://www.mcmaster.com/hose/hose-...ize~3-4/air-hose-with-male-threaded-fittings/

On the propane tank I'm using all sch 40 stainless ******* and medium pressure (300psi) stainless fittings: https://www.mcmaster.com/stainless-...ure-stainless-steel-threaded-pipe-fittings-8/

Should be a pretty safe setup.

-Jamie M.
 

RustyJunk

Well-known member
Joined
Jun 11, 2018
Messages
274
Location
Pasco Fl.
If you want steel pipe that's rated stay clear of the box store junk because they just stock the cheapest stuff they can get and every month it's different. Go to a plumbing or industrial supply and get the correct material for your application along with the fittings you need all in one shot.
 