Black pipe offset fitting

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
Is there a black gas pipe offset fitting? A fitting that will run the pipe closer to the wall by say 1/2" to 1"?

Right now the sheetrock will push against the gas pipe and not get flush to the the rest of the sheetrock.


1c06ed91bee0435c5c409b0259420e39.jpg

Sent from my iPhone using Tapatalk
 

Attachments

  • 1c06ed91bee0435c5c409b0259420e39.jpg
    1c06ed91bee0435c5c409b0259420e39.jpg
    132.5 KB · Views: 0
To avoid these ads, REGISTER NOW!

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
Opposing 45s is a good idea since you can twist the first one to the side to move it back to the wall and then straighten it out with the second and keep going. You will have moved the pipe line an inch or two over but you will be closer to the wall
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,857
Location
Desert SW
Opposing 45s is a good idea since you can twist the first one to the side to move it back to the wall and then straighten it out with the second and keep going. You will have moved the pipe line an inch or two over but you will be closer to the wall

:thumbup: Or using 2 90's to angle up a pitched roof. Once I learned that trick running pipe got alot easier.

Now it's just getting the newbies to use the right pipe - black iron for gas, galvanized for water. No switching around! :rant:
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
Great ideas guys. Got a street 90 and regular 90 turned so that im on stud center for the remainder of my run.

d6e44e5c6fb03845b8a3b0b260a67075.jpg




Sent from my iPhone using Tapatalk
 

Attachments

  • d6e44e5c6fb03845b8a3b0b260a67075.jpg
    d6e44e5c6fb03845b8a3b0b260a67075.jpg
    115.7 KB · Views: 0

bobbyjean

Well-known member
Joined
Aug 25, 2017
Messages
319
Location
hudson valley n.y.
a valve behind a fixed wall, what good is it...the handle is keeping it off the wall....reposition it if possible...you could relocate it to make it workable..or add access door
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
Bobbyjean: It’s the 3/4” vertical pipe that is causing the protrusion. It’s not lined up parallel to the wall. It’s pushing inward toward the inside of the home.

I’m going to put another valve at the new location. About 5’ over. The valve in the picture will be left in the on position.



Sent from my iPhone using Tapatalk
 

bobbyjean

Well-known member
Joined
Aug 25, 2017
Messages
319
Location
hudson valley n.y.
branimal: ok...i'm guessing you have no access to anything from below..if that's the case
you could strap the riser fast to the wall...maybe halfway up the rise....can you shut gas down to remove that valve?
 
To avoid these ads, REGISTER NOW!

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,452
Location
Beautiful Southern Maryland
There is no way I would leave the valve covered up in the wall. It might start leaking through the stem and you would never know. I would almost have to bet it is not code either.

Turn the gas off and get rid of the valve in my opinion.
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
There is no way I would leave the valve covered up in the wall. It might start leaking through the stem and you would never know. I would almost have to bet it is not code either.

Turn the gas off and get rid of the valve in my opinion.



Good point... you think the valve is more likely to leak than the fittings?


Sent from my iPhone using Tapatalk
 

b-boy

Well-known member
Joined
Oct 2, 2013
Messages
2,158
Location
Buffalo NY
I agree on the valve. I'd be nervous leaving it like that.

I always thought that it was a no-no to put any gas pipe fittings behind drywall. If they leak they'll create pockets of gas that you may not smell, that won't dissipate, and that can increase the volitility of an explosion.
 

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,963
Location
Southern Indiana
I agree on the valve. I'd be nervous leaving it like that.

I always thought that it was a no-no to put any gas pipe fittings behind drywall. If they leak they'll create pockets of gas that you may not smell, that won't dissipate, and that can increase the volitility of an explosion.

I've not seen that happen, but I have definitely seen problems with gas leaks in wall cavities that can't be accessed. The most common fix is to shut off the gas to the structure and have a plumber cut the offending area of piping loose from the system and repipe in an exposed manner. Typically most plumbers shy away from tearing out drywall if there's anyway to avoid it.

Best solution might be to have an access door.

Phil
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
You can not bury a junction box so I'm thinking that you wouldn't be able to bury a a shut off valve in a wall. Wouldn't do it in my home.
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
Advice will be taken guys. I’ll get rid of the inaccessible shutoff valve.