snowdust2
Active member
I am running 200' of 1 1/4" gas line to my shop that will run a 75k btu Hot Dawg heater. Inside the shop I ran 1/2" black pipe about 30' to stub out where I'll connect the heater. I was looking at the manual and if I read it right I am real close to min CFH due to the 30' run of black pipe. Can someone with more knowledge than me take a look at the pic and see if they agree? I see it as I need 71.4 and I'll be at 73 if I am 30'. (I need to measure and may be closer to 35') Wondering if I should change it out to 3/4 before I drywall. Thanks!