Boiler check valve?

Brentd2183

Active member
Joined
Dec 27, 2009
Messages
25
Location
Long Island NY
Sister in laws house, complaints of funny tasting water,plumber came over and said the boiler needs a check valve. The water in the heating circuit is back flowing into the cold water supply. They also have the brown radiate heat pex tubing running for most of their domestic water lines. I think the taste is from the 90 year old water main from the street that is corroded and due to be replaced next year. Gas boiler, single zone, forced hot water baseboard heaters. Does this plumbing look right to you? Does it need a check valve?
 

Attachments

  • IMG_8500.jpg
    IMG_8500.jpg
    314.3 KB · Views: 21
  • IMG_8501.jpg
    IMG_8501.jpg
    345.2 KB · Views: 22
  • IMG_8502.jpg
    IMG_8502.jpg
    378.2 KB · Views: 21
  • IMG_8509.jpg
    IMG_8509.jpg
    397.1 KB · Views: 21
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,743
Location
Long Island
I highly doubt water is back-flowing through the regulator, though there is supposed to be a check valve there.
 
OP
B

Brentd2183

Active member
Joined
Dec 27, 2009
Messages
25
Location
Long Island NY
That was my thought, full city water pressure pushing into the boiler, how could the baseboard water go backwards. Also correct me if I'm wrong but I thought the two waters never touch? I assume an indirect coil type heat transfer and the water going to the boiler is just to fill the system. They have a separate hot water heater.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
There should be an atmospheric flow check -- it's sort of like one on a sprinkler system. Boilers do pressurize the water in them and if the pressure drops in the domestic -- the boiler water can flow in reverse.

I'm sure when the original boiler was installed -- it had one.
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,144
Location
Niagara Region, Ontario, Canada
heated water creates a lot of hydraulic pressure ( think radiator cap at 15LBS .) a hot water tank can explode if it is sealed & doesn't have a relief valve installed .
It needs a check valve as well as be sure the expansion tank is doing it's thing and not water logged or split bladder
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,743
Location
Long Island
You can see the relief valve next to the expansion tank. It should be blowing out a burst of steaming water if the pressure downstream of the regulator exceeds 30PSI.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,889
Location
Fargo, ND
Minimally you need a Watts 9D. Some jurisdictions require and RPZ back flow preventer.
 