I am renovating a 1958 brick ranch. The house has baseboard/floor propane fueled boiler heat and forced air AC in the attic. Both units are from the early 90s and they do work, but are obviously dated. We are doing a full renovation of the house and are considering doing away with the boiler and central AC to go with minisplits. We are in NW Ohio. What do you guys think? Stick with the boiler or go to minisplits?
I wouldn't ditch the boiler for mini splits.
Also wonder WTF the "noisy mini split" crowd is complaining about. Unless it is in turbo mode, I can't hear it operate.
If the boiler is cast iron, it's probably fine *as long as it's piped correctly*. Return water temperature must be 140 degrees or higher. Boiler instruction manuals come with piping diagrams.
The attic is the absolute worst place to put HVAC. If equipment replacement is on the table, I'd make sure that the ductwork is all sealed and insulated... or spray foam the attic and make it conditioned space.
If "renovation" also includes doing stuff like adding insulation, windows and so forth to improve the building envelope, that will alter the HVAC load. If no changes are made to the hydronic stuff and the building is made tighter/more insulated, this will aggravate short cycling of the boiler and keep water temperature down, which increases fuel use and flue gas condensation.
The radiators/fin tube is sized for the heat loss, then the boiler is sized for the radiation. They go hand in hand.
I do not see boilers running residential stuff at 180 degrees, which is the common assumption for water temp and btu capacity of the radiation.
There are books/resources to figure out the btu capacity of your installed radiation. You will also need a room by room load calculation.
If you want to "save money" the boiler stuff has to be sized properly.
Either find someone that knows how to do it, or do it yourself.
Good luck.