We just moved into our new digs back in late July. Now we're getting a big storm and I don't have a clue about this, so here goes...
We have a well for water with a 50gal pressure tank, and a steam boiler. If we lose power, can I still run my boiler without the well being on. I have a generator, but not the correct connections for a 240v well. I know it's a 'sealed' system of sorts, but I'm worrying about the pressure and running it out of water.
Thanks, bob
 
To avoid these ads, REGISTER NOW!

pascone10

New member
Joined
Feb 20, 2013
Messages
3
There should be a sight glass on the side of that Boiler. You need to keep the water level above the Minimum boiler water level ( should be a sticker on the boiler or the measurement will be in the manual)

Is there a make up water feed on this boiler? Is it turned on?

Also do you have Low Water Cutoff devices? Check them to make sure they are working properly. If you don't PLEASE ADD THEM!

The last thing you want to do is dry fire that boiler.
 

dogdas

Well-known member
Joined
Oct 24, 2014
Messages
94
It should have a low water cutoff installed and if it does then yes you can run it. Only if you have leaks will your boiler need water.
 
OP
B

bobemmerich

Well-known member
Joined
Aug 23, 2009
Messages
1,611
Location
Middletown, Ct.
Sight glass and low cutoff is there. Ok. I'm hoping I don't have to do it, but IF I do, ok.
Trying to figure how to hook up the 15A 240v well circuit without a transfer switch...
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Sight glass and low cutoff is there. Ok. I'm hoping I don't have to do it, but IF I do, ok.
Trying to figure how to hook up the 15A 240v well circuit without a transfer switch...

You can shut the main off at the panel then backfeed through a 2p breaker fed by your generator,not a big deal.
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
Sight glass and low cutoff is there. Ok. I'm hoping I don't have to do it, but IF I do, ok.
Trying to figure how to hook up the 15A 240v well circuit without a transfer switch...

Steam does use a little water, but with a low cutoff switch it is safe to run. Anyway, you can probably go for several days without needing any makeup water.
 

roscoe2000

Well-known member
Joined
Sep 22, 2009
Messages
264
Location
Seat Pleasant Md
Your other problem you will be needing to supply power to the boiler circuit, stat, condensate pump and burner.
 