Bonded or split neutral on unique application

Coyote556

Well-known member
Joined
May 6, 2013
Messages
108
Location
The Show-Me State
I am installing a small subpanel on my utility pole. It is a four space, main lug, sub panel. This panel will be on the same panel as the meter.

The meter is a 200a disconnect with "Triple tap." Similar to Milbank U9647N-RL-200

http://www.cesco.com/b2c/product/Milbank-U9647N-RL-200-Ringless-3-Wire-Meter-Main/648365

It has a 200a main breaker that feeds a triple lug. One of those lugs feeds my house, one feeds my barn, and the third will feed this subpanel on the utility pole. From the subpanel I am running a 20a GFCI outlet and possibly another circuit on the pole later on.

My question is about the neutral and ground. Should they be bonded inside the subpanel or split? I know if it was a separate structure, the would be split, but since it is on the same pole and literally about 10" from the meter, I did not know.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Since the panel is beyond the main breaker, it is a "subpanel" and needs separated neutral and ground supplied to it. Is this new panel capable of 200 amps? If not I think it would not be wise to supply it with a 200 amp main breaker.

Charles
 