Well-known member
Calling on the electricians... I had my heater inspected today mechanical passed but he made one comment that I want to follow through on. He said to Bond the gas line since there was csst connecting the gas line to the heater.
There is other csst in the house so I want to get it done. I need a bonding clamp and some 6ga copper wire. I can bond it at the panel since it is right next to my water heater. All of my water lines are bonded but the gas is not. My question is this. Since my panel is quite full would it be acceptable to use a split nut on one of the 4 6 gauge ground wire going into the panel to make the bond to the black iron pipe?
There is other csst in the house so I want to get it done. I need a bonding clamp and some 6ga copper wire. I can bond it at the panel since it is right next to my water heater. All of my water lines are bonded but the gas is not. My question is this. Since my panel is quite full would it be acceptable to use a split nut on one of the 4 6 gauge ground wire going into the panel to make the bond to the black iron pipe?