Bonding CSST

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,233
Location
Maryland
I see a lot about the need to bond or ground CSST. I have some that extends my black pipe to the garage. It's all exposed. And it's connected directly to the black pipe system that is grounded. So why would I need to add another ground to the CSST?

Comments?
Tom
 
To avoid these ads, REGISTER NOW!

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,915
Location
Southern Indiana
You need to find the manufacture's current instructions for your product an insure that your installation complies with that book. If you do a google search, you should be able to find a pdf version of it online.

My guess is you'll find a description on bonding that will inform you what size bonding wire you need, where to route it and how to attach it to your piping.

The previous responder is correct. The issue with CSST has been that if it becomes energized due to a lightning strike it may burn through causing a gas leak and ignition source simultaneously. Bad outcomes have occurred.

All things being equal, I'd rather have black pipe...but that's just my opinion.

Phil
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Good luck...I would have went with CSST myself...but after I could not find an easy to understand description of EXACTLY what I needed to do, I figured it was cheaper, easier and "bulletproof" to just go with Black Pipe.

Unless there's some requirement or reason your going with CSST...I'd say by the time you figure out what & how you need to ground it, you would be done your black pipe install.
 

BillChoneser

Member
Joined
Oct 29, 2015
Messages
5
If the rest of the house uses CSST and is already bonded from the manifold wouldn't a new CSST run be the obvious choice then over black pipe?
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Bottom line......... a clamping kit and a small section wire is all that's needed.

If it were only that simple...
When I looked into it, my understanding was, it needed to be 6 ga copper, and bonded INTO an approved panel. So in my case that meant a 25' run of 6 ga copper wire into my sub-panel. 25' of 6ga copper + CSST Tubing + CSST Fittings = Way more money then good ol steel pipe.

Easier to run - Yes; Cheaper - No

Sprinkle in the whole "This is new, I hope its right, nobody seems to know" aspect...black pipe was and is the industry gold standard for longer then I've been alive. Information on black pipe is readily available, everybody knows how to use it and what to do to make it right.
 
To avoid these ads, REGISTER NOW!
OP
T

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,233
Location
Maryland
So...the garage is attached. I realize the problem with lightning strikes. My question is since the black pipe system to which the CSST is attached is already bonded/grounded, why would the CSST have to be additionally bonded/grounded?

I have been thinking of replacing with black pipe, but this would not be simple. Anything can be done.

Tom
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,184
Location
The UP, God's country
Since the system is already defined bonded, you don't need a redundant bond.

The data sheet shipped with the termination fittings show that either the fitting or the upstream iron pipe have to be bonded.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
If it were only that simple...
When I looked into it, my understanding was, it needed to be 6 ga copper, and bonded INTO an approved panel.

The panel is one option for bonding. Mine is bonded directly to the UFER ground, which is another option.
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
So...the garage is attached. I realize the problem with lightning strikes. My question is since the black pipe system to which the CSST is attached is already bonded/grounded, why would the CSST have to be additionally bonded/grounded?

I have been thinking of replacing with black pipe, but this would not be simple. Anything can be done.

Tom

From what I gather....again I'm no pro, nor do I pretend to be one. This is just my understanding of the situation after doing 2 weeks of research & reading.... but WHERE the ground is makes a difference with CSST...with black pipe, a ground anywhere is good enough, for the purposes of heating, the chassis bond in the furnace is sufficient when using all black pipe. CSST requires additional bonding, and that's where it gets messy...just cant slap the bond at any ol place...for lightning protection I think the bond needs to be towards the exterior end of the CSST Run.

CSST seems to be a great product...but its still "too new" for me. We are only talking bonding in this thread, but there are a host of other considerations to make to do a correct CSST install....tube protection in certain areas, etc..
 

Champ128

Active member
Joined
May 3, 2015
Messages
33
Every manufacturer has different bonding requirements. What pipe are you intending to use?
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Good luck...I would have went with CSST myself...but after I could not find an easy to understand description of EXACTLY what I needed to do, I figured it was cheaper, easier and "bulletproof" to just go with Black Pipe.

Unless there's some requirement or reason your going with CSST...I'd say by the time you figure out what & how you need to ground it, you would be done your black pipe install.

Not hardly.

It is in the installation manual and you don't have to read to understand it.

They have pictures.
 