Box Cover flush with Box vs. Drywall

Reborn

Well-known member
Joined
Dec 31, 2017
Messages
113
Location
SoCal
I know ideally the cover should be flush with the box, not the drywall. I removed a standard porcelain light fixture, and you can see it was flush on drywall (discolored drywall) rather than on the box. How critical is it to take a blade around my new cover and enable it to sit flush against the box instead of the drywall? There is a good 1/2" between drywall surface and box surface.

And as an aside, is the fact that I "tampered" with the receptacle to drill 2 holes for the screws anything to be concerned about for code compliance?

Thanks in advance.

attachment.php


attachment.php
 

Attachments

  • IMG_0475.jpg
    IMG_0475.jpg
    69.9 KB · Views: 169
  • IMG_0476.jpg
    IMG_0476.jpg
    77.4 KB · Views: 171
To avoid these ads, REGISTER NOW!

Kevin Essiambre

Well-known member
Joined
May 1, 2014
Messages
208
Location
Ottawa, Ontario, Canada
I don't know about NEC, but the Canadian code permits the box to be back a little bit only on non-flammable finishing.

If it's drywall, I wouldn't worry too much about it.

If you are worried, Arlington makes a box extender for that. Part number BE1R
4e3c40babd982e68feed55174b036f97.jpg


Sent from my SM-G920W8 using Tapatalk
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
There is a good 1/2" between drywall surface and box surface.

2017 NEC
314.20 Flush-Mounted Installations.
Installations within or behind a surface of concrete, tile, gypsum, plaster, or other noncombustible material, including boxes employing a flushtype cover or faceplate, shall be made so that the front edge of the box, plaster ring, extension ring, or listed extender will not be set back of the finished surface more than 6 mm (1∕4 in.).
Installations within a surface of wood or other combustible surface material, boxes, plaster rings, extension rings, or listed extenders shall extend to the finished surface or project therefrom.
 
OP
R

Reborn

Well-known member
Joined
Dec 31, 2017
Messages
113
Location
SoCal
I don't know about NEC, but the Canadian code permits the box to be back a little bit only on non-flammable finishing.

If it's drywall, I wouldn't worry too much about it.

If you are worried, Arlington makes a box extender for that. Part number BE1R
4e3c40babd982e68feed55174b036f97.jpg


Sent from my SM-G920W8 using Tapatalk
Based on the next reply, looks like that is the case with NEC as well. Thanks for the box extender reference, but I will either leave it or remove the drywall as those would be the easier/quicker options. :)

2017 NEC
314.20 Flush-Mounted Installations.
Installations within or behind a surface of concrete, tile, gypsum, plaster, or other noncombustible material, including boxes employing a flushtype cover or faceplate, shall be made so that the front edge of the box, plaster ring, extension ring, or listed extender will not be set back of the finished surface more than 6 mm (1∕4 in.).
Installations within a surface of wood or other combustible surface material, boxes, plaster rings, extension rings, or listed extenders shall extend to the finished surface or project therefrom.

Excellent, thank you for that. I will actually measure the offset and see how far back the box edge sits. That will determine whether I leave it or remove the drywall. :beer:
 