Box fill confusion
Currently planning electrical for my 40 x 40 metal building.
I am running 4 circuits 14ga THHN through 3/4 EMT into junction box represented by the blue square.
8 CCC in conduit 70% derate so 25 amps allowed at 90C 25a x 0.7= 17.5 amps
15 amp breaker due to max allowable over current protection
The question is do the two circuits that run through the box (no splices) count as 4 or 8?
This will most likely be going into a 3-gang box may upgrade to 4-gang just because.
Does everything look up to NEC code? (Clay county Florida)
Did I miss anything?
Sorry about the crude pic and huge post if I have learned anything here It's that insufficient information is not an option.