Innovate1
Well-known member
Looking at box fill for wiring. Here minimum size wire is #12.
18 cu in box (cheapest plastic one I think) allows 8 conductors - that's 2 for the device (switch or receptacle), 1 for ground leaving 5, which allows 2 conductors in and 2 out.
20 cu in box allows 8.9 so no more allowed - just more working space to make things a bit easier.
22 in box allows 9.8 conductors - but has integral clamps which count as 1 so still not allowed to have more runs.
So it appears to get more than an input and output cable (and I want neutral in all boxes) I need to go to a 2 gang box with single extension ring.
Dual box is 32 cu in - this allows 14 conductors. Take away 2 for the device, 1 for ground, and one for clamps and that leaves 10. Enough for 5 two conductor NM cables.
For a dual box with two devices I could have 4 cables. And the volume of the extension ring might allow more.
Am I right on this? Thinking I should use 20 cu in as my minimum size and probably need several dual with single rings and some dual with dual rings...
18 cu in box (cheapest plastic one I think) allows 8 conductors - that's 2 for the device (switch or receptacle), 1 for ground leaving 5, which allows 2 conductors in and 2 out.
20 cu in box allows 8.9 so no more allowed - just more working space to make things a bit easier.
22 in box allows 9.8 conductors - but has integral clamps which count as 1 so still not allowed to have more runs.
So it appears to get more than an input and output cable (and I want neutral in all boxes) I need to go to a 2 gang box with single extension ring.
Dual box is 32 cu in - this allows 14 conductors. Take away 2 for the device, 1 for ground, and one for clamps and that leaves 10. Enough for 5 two conductor NM cables.
For a dual box with two devices I could have 4 cables. And the volume of the extension ring might allow more.
Am I right on this? Thinking I should use 20 cu in as my minimum size and probably need several dual with single rings and some dual with dual rings...