600SL
Well-known member
First a sanity check here. I believe I need a 22.5 CU for my reversible fan based on"
Fan has 4 18 ga wires - which dont count.
4 12 gage wires coming into the box
4 12 gage wires leaving the box going to another fan
1 ground
1 hanging hook that passes through the box
Total = 10x2.25 = 22.5
The hook just passes through the box. The box does not bear the weight of the fan.
12 ga wire is required because of the CB power is coming off.
OK so I go to look for an octagon box and I come up with HD which has them in stock but you have to buy a case of 25 or Platt who doesn't have them in stock and they are really expensive if they ever get them.
But HD and pretty much everywhere else has 4" octagon boxes of the same 2.125" depth but for some reason only rated at 20 cu.
https://www.platt.com/platt-electri...el-City/54171-1-2-3-4/product.aspx?zpid=57694
I know I can use an extension ring but I kind of don't like them.
Fan has 4 18 ga wires - which dont count.
4 12 gage wires coming into the box
4 12 gage wires leaving the box going to another fan
1 ground
1 hanging hook that passes through the box
Total = 10x2.25 = 22.5
The hook just passes through the box. The box does not bear the weight of the fan.
12 ga wire is required because of the CB power is coming off.
OK so I go to look for an octagon box and I come up with HD which has them in stock but you have to buy a case of 25 or Platt who doesn't have them in stock and they are really expensive if they ever get them.
But HD and pretty much everywhere else has 4" octagon boxes of the same 2.125" depth but for some reason only rated at 20 cu.
https://www.platt.com/platt-electri...el-City/54171-1-2-3-4/product.aspx?zpid=57694
I know I can use an extension ring but I kind of don't like them.