I am adding a full set up of receptacles, lights, AC etc and am trying to figure out my breaker box location and the electric feed to my shop is next to the garage door, it is just a 2 gang box with the wire pulled through conduit.

600dbc7f27ff09fc915a7ce23d4123b9.jpg

I would like to move it to the side wall so that I can eventually install a larger garage door. If I do that will I have to move where the feed line comes into the shop or can I run the feed line through the studs inside?

Thanks for the help.
.

Sent from my SM-G920V using Tapatalk
 
To avoid these ads, REGISTER NOW!

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
How much larger of a garage door are you planning? Looks like you could add a foot without issue.

You would probably still need a junction box where the PVC comes in. Running through studs with PVC would add too many bends.
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
Just a foot bigger. I am also concerned about having the box right next to the garage door.

Sent from my SM-G920V using Tapatalk
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
OK - You need 30" width of clear space. I forgot about the garage door track being in the way so you can't put a panel there.

Keeping that box as a junction box shouldn't be an issue - it will just have a stud on each side of it. Convert to NM cable running through joists to new panel then cover with drywall. You will also need a GEC - two grounding rods if you don't have a concrete UFER.

What is running through conduit now? Hopefully you can get 4 conductors in it. 10 gauge would be max if that is 1/2" PVC.
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
OK - You need 30" width of clear space. I forgot about the garage door track being in the way so you can't put a panel there.

Keeping that box as a junction box shouldn't be an issue - it will just have a stud on each side of it. Convert to NM cable running through joists to new panel then cover with drywall. You will also need a GEC - two grounding rods if you don't have a concrete UFER.

What is running through conduit now? Hopefully you can get 4 conductors in it. 10 gauge would be max if that is 1/2" PVC.
That box is the only power run to the shop, I am guessing I am going to have to install some grounding rods. And I think the conduit is just near the building, I think the wire might be direct bury. Thanks for the help!

Sent from my SM-G920V using Tapatalk
 
Last edited:
To avoid these ads, REGISTER NOW!

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,101
Location
Marina del Rey
If that 1 box is your sole garage service, you will likely need to begin by running a new cable from a new breaker on your main panel; I'd recommend that breaker be 100-amps 220V, to feed a 100-amp garage sub panel, if you expect to power a machine, compressor or welder.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Generally your subpanel in garage is mostly determined on WHERE the feed needs to come from the house. Presume you are pursuing BURIED from house ??

How far ?? Any things blocking best route to garage ??

Key thing you need to remember is keeping area CLEAR around the breaker box. See recent GJ thread that covers this very well.

Somewhat the "standard GJ solution" for powering detached garages is MHF Al 2-2-2-4 when garage is fairly close, buried in 2" conduit, then also in conduit to the panel. This is Mobile Home Feeder aluminum (approx $1.50/ft) that will give you 90A in garage (ie put that breaker in house), and nice solution for garage would be 100A panel w/ main breaker and 20 spaces.

GJ Sparky's will give you great detailed advice with the right information.
 